ION9000 measurement accuracy and time synchronization

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 measurement accuracy and time synchronization
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2022-03-23 08:08 AM . Last Modified: ‎2022-03-23 08:08 AM

0 Likes
4
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 08:08 AM

ION9000 measurement accuracy and time synchronization

Hi All, I have two inquiries about ION9000

 

1. Would the measurement accuracy be lower when ION9000 is doing half-cycle true RMS readings? Or the accuracy is as good as the datasheet states?

 

2. If there are several ION9000 in the network and we use PTP to do the time synchronization, would all the meters sample and update the measurement at the same time?

 

Thank you.

Labels
  • Labels:
  • ION9000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-23 10:54 AM

2 Likes
3
1738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 10:54 AM

1. The ION9000 Power Quality Aggregator (PQA) Module complies to IEC61000-4-30 Class A.


https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=PowerQualityAggregatorModu...

 

The PQA module has six half-cycle voltage RMS outputs that meet the required "+/-0.1% of Udin" (in the range of 10% to 150% of Udin) accuracy spec required for Class A.


https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=7EN72%E2%80%930185%...

 

The high-speed powermeter module outputs do not perform the same prescribed measurement alignment algorithm specified and required by the 4-30 standard.

 

2. Mostly yes. ION9000 meters correctly configured for PTP (Clock source = COMM, etc) will produce synchonized and time-aligned IEC61000-4-30 Class A readings (also all 1-second measurements will be aligned). The alignment time accuracy for Class A is +/- 1cycle.

 

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=ClockModule-3E8613C1&lang=...

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-23 10:54 AM

2 Likes
3
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 10:54 AM

1. The ION9000 Power Quality Aggregator (PQA) Module complies to IEC61000-4-30 Class A.


https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=PowerQualityAggregatorModu...

 

The PQA module has six half-cycle voltage RMS outputs that meet the required "+/-0.1% of Udin" (in the range of 10% to 150% of Udin) accuracy spec required for Class A.


https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=7EN72%E2%80%930185%...

 

The high-speed powermeter module outputs do not perform the same prescribed measurement alignment algorithm specified and required by the 4-30 standard.

 

2. Mostly yes. ION9000 meters correctly configured for PTP (Clock source = COMM, etc) will produce synchonized and time-aligned IEC61000-4-30 Class A readings (also all 1-second measurements will be aligned). The alignment time accuracy for Class A is +/- 1cycle.

 

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=ClockModule-3E8613C1&lang=...

Tags (1)
  • Tags:
  • english
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2022-03-24 07:21 AM

0 Likes
2
1701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-24 07:21 AM

Hi @DanL,

 

Many thanks for your information. Would like to check if my understanding is correct.

 

  1. When ION9000 is doing half-cycle true RMS reading, we only can say the accuracy of the “voltage” measurement meets the accuracy spec required for IEC 61000-4-30 Class A (+/-0.1%). But other parameters such as frequency and power, we cannot make the same statement (accuracy probably would be lower than the value listed on the datasheet?)
  2. It’s clear that if we set up the PTP time synchronization correctly, the alignment time accuracy would be +/- 1cycle when the meters are doing a 1-second measurement. How about when all the meters are doing half-cycle true RMS reading? Would all the meters sample and update the measurement at the same time and what would be the uncertainty?

 

Thank you.

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-24 08:42 AM

1 Like
1
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-24 08:42 AM

 

  1. All six of the provided 4-30 Class A One-Cycle-Every-Half-Cycle true RMS, phase-aligned voltage measurements (Urms[½]) provided by the PQA module are designed and tested to meet the required accuracy for IEC 61000-4-30 Class A (+/-0.1% of Udin).
    The other One-Cycle-Every-Half-Cycle parameters originating from other ION modules (such as frequency and power from the HS Power Meter Module) are not designed to nor specified by 4-30 and thus have no official reference. However, because all these parameters are used by the calculations for longer intervals (1Second, 150/180Cycle, and 10minute), we do know that (under steady state) these values are typically just as accurate.
  2. The six high-speed phase-aligned voltage measurements (Urms[½]) from the PQA module are specifically designed to be repeatable between time synchronized devices. The other HS values will not provide phase-aligned measurement windows, but will still be synchronized to within +/-1cycle (while using PTP). 
Tags (1)
  • Tags:
  • english
Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2022-03-25 07:15 AM

0 Likes
0
1667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-25 07:15 AM

Hi @DanL 

 

It is much clear now. Many thanks for your help.

 

best regards

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of