Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

ION9000 measurement accuracy and time synchronization

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 measurement accuracy and time synchronization
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
292
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
71
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Stuart_Cheng
Lieutenant Stuart_Cheng Lieutenant
Lieutenant

Posted: ‎2022-03-23 08:08 AM . Last Modified: ‎2022-03-23 08:08 AM

0 Likes
4
920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 08:08 AM

ION9000 measurement accuracy and time synchronization

Hi All, I have two inquiries about ION9000

 

1. Would the measurement accuracy be lower when ION9000 is doing half-cycle true RMS readings? Or the accuracy is as good as the datasheet states?

 

2. If there are several ION9000 in the network and we use PTP to do the time synchronization, would all the meters sample and update the measurement at the same time?

 

Thank you.

Labels
  • Labels:
  • ION9000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-23 10:54 AM

2 Likes
3
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 10:54 AM

1. The ION9000 Power Quality Aggregator (PQA) Module complies to IEC61000-4-30 Class A.


https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=PowerQualityAggregatorModu...

 

The PQA module has six half-cycle voltage RMS outputs that meet the required "+/-0.1% of Udin" (in the range of 10% to 150% of Udin) accuracy spec required for Class A.


https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=7EN72%E2%80%930185%...

 

The high-speed powermeter module outputs do not perform the same prescribed measurement alignment algorithm specified and required by the 4-30 standard.

 

2. Mostly yes. ION9000 meters correctly configured for PTP (Clock source = COMM, etc) will produce synchonized and time-aligned IEC61000-4-30 Class A readings (also all 1-second measurements will be aligned). The alignment time accuracy for Class A is +/- 1cycle.

 

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=ClockModule-3E8613C1&lang=...

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-23 10:54 AM

2 Likes
3
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-23 10:54 AM

1. The ION9000 Power Quality Aggregator (PQA) Module complies to IEC61000-4-30 Class A.


https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=PowerQualityAggregatorModu...

 

The PQA module has six half-cycle voltage RMS outputs that meet the required "+/-0.1% of Udin" (in the range of 10% to 150% of Udin) accuracy spec required for Class A.


https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=7EN72%E2%80%930185%...

 

The high-speed powermeter module outputs do not perform the same prescribed measurement alignment algorithm specified and required by the 4-30 standard.

 

2. Mostly yes. ION9000 meters correctly configured for PTP (Clock source = COMM, etc) will produce synchonized and time-aligned IEC61000-4-30 Class A readings (also all 1-second measurements will be aligned). The alignment time accuracy for Class A is +/- 1cycle.

 

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=ClockModule-3E8613C1&lang=...

Tags (1)
  • Tags:
  • english
Reply
Stuart_Cheng
Lieutenant Stuart_Cheng Lieutenant
Lieutenant

Posted: ‎2022-03-24 07:21 AM

0 Likes
2
861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-24 07:21 AM

Hi @DanL,

 

Many thanks for your information. Would like to check if my understanding is correct.

 

  1. When ION9000 is doing half-cycle true RMS reading, we only can say the accuracy of the “voltage” measurement meets the accuracy spec required for IEC 61000-4-30 Class A (+/-0.1%). But other parameters such as frequency and power, we cannot make the same statement (accuracy probably would be lower than the value listed on the datasheet?)
  2. It’s clear that if we set up the PTP time synchronization correctly, the alignment time accuracy would be +/- 1cycle when the meters are doing a 1-second measurement. How about when all the meters are doing half-cycle true RMS reading? Would all the meters sample and update the measurement at the same time and what would be the uncertainty?

 

Thank you.

Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-03-24 08:42 AM

1 Like
1
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-24 08:42 AM

 

  1. All six of the provided 4-30 Class A One-Cycle-Every-Half-Cycle true RMS, phase-aligned voltage measurements (Urms[½]) provided by the PQA module are designed and tested to meet the required accuracy for IEC 61000-4-30 Class A (+/-0.1% of Udin).
    The other One-Cycle-Every-Half-Cycle parameters originating from other ION modules (such as frequency and power from the HS Power Meter Module) are not designed to nor specified by 4-30 and thus have no official reference. However, because all these parameters are used by the calculations for longer intervals (1Second, 150/180Cycle, and 10minute), we do know that (under steady state) these values are typically just as accurate.
  2. The six high-speed phase-aligned voltage measurements (Urms[½]) from the PQA module are specifically designed to be repeatable between time synchronized devices. The other HS values will not provide phase-aligned measurement windows, but will still be synchronized to within +/-1cycle (while using PTP). 
Tags (1)
  • Tags:
  • english
Reply
Stuart_Cheng
Lieutenant Stuart_Cheng Lieutenant
Lieutenant

Posted: ‎2022-03-25 07:15 AM

0 Likes
0
827
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-03-25 07:15 AM

Hi @DanL 

 

It is much clear now. Many thanks for your help.

 

best regards

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.