Hi All, I have two inquiries about ION9000
1. Would the measurement accuracy be lower when ION9000 is doing half-cycle true RMS readings? Or the accuracy is as good as the datasheet states?
2. If there are several ION9000 in the network and we use PTP to do the time synchronization, would all the meters sample and update the measurement at the same time?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
1. The ION9000 Power Quality Aggregator (PQA) Module complies to IEC61000-4-30 Class A.
The PQA module has six half-cycle voltage RMS outputs that meet the required "+/-0.1% of Udin" (in the range of 10% to 150% of Udin) accuracy spec required for Class A.
The high-speed powermeter module outputs do not perform the same prescribed measurement alignment algorithm specified and required by the 4-30 standard.
2. Mostly yes. ION9000 meters correctly configured for PTP (Clock source = COMM, etc) will produce synchonized and time-aligned IEC61000-4-30 Class A readings (also all 1-second measurements will be aligned). The alignment time accuracy for Class A is +/- 1cycle.
Link copied. Please paste this link to share this article on your social media post.
1. The ION9000 Power Quality Aggregator (PQA) Module complies to IEC61000-4-30 Class A.
The PQA module has six half-cycle voltage RMS outputs that meet the required "+/-0.1% of Udin" (in the range of 10% to 150% of Udin) accuracy spec required for Class A.
The high-speed powermeter module outputs do not perform the same prescribed measurement alignment algorithm specified and required by the 4-30 standard.
2. Mostly yes. ION9000 meters correctly configured for PTP (Clock source = COMM, etc) will produce synchonized and time-aligned IEC61000-4-30 Class A readings (also all 1-second measurements will be aligned). The alignment time accuracy for Class A is +/- 1cycle.
Link copied. Please paste this link to share this article on your social media post.
Hi @DanL,
Many thanks for your information. Would like to check if my understanding is correct.
Thank you.