ION9000 Meter Configuration

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 Meter Configuration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa356640
Ensign sesa356640 Ensign
Ensign

Posted: ‎2020-08-31 10:16 PM

0 Likes
7
2508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-08-31 10:16 PM

ION9000 Meter Configuration

Hi,

Meter Model - ION9000

Connection - 4W - Wye

PT Ration - 400/110 (LV system)

 

For configuring ION9000 meter - PT Ratio & Nominal Voltage, whether i need to provide L-L voltage or L-N voltage.

Also share any document suggesting the above.

 

Regards,

Aravind

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2020-09-01 12:15 AM

1 Like
1
2502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-01 12:15 AM

Hi,

please see: https://www.se.com/ww/en/faqs/FA243523/

I am pretty sure this applies also to ION9000.

 

Best regards

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2020-09-01 12:15 AM

1 Like
1
2503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-01 12:15 AM

Hi,

please see: https://www.se.com/ww/en/faqs/FA243523/

I am pretty sure this applies also to ION9000.

 

Best regards

Tags (1)
  • Tags:
  • english
Reply
sesa356640
Ensign sesa356640 Ensign
Ensign

Posted: ‎2020-09-01 04:01 AM

0 Likes
0
2500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-01 04:01 AM

Thanks 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-09-01 08:07 AM

0 Likes
4
2496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-09-01 08:07 AM

Hello @sesa356640  and @Szymon_Hochół ,

 

With the ION9000 there is a newer setup register that can force the Sag/swell module to use the VLL inputs "Use Vll Always". If this setting is used, the VLL should be used as nominal. Note that the nominal voltage is also used in a few other places. 

 

If not using this setting, then the details in the KB apply.

 

Regards,

Charles

 

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
geir_eas_no_bfo
Lt. Commander geir_eas_no_bfo
Lt. Commander

Posted: ‎2022-02-22 12:55 AM

0 Likes
3
2164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-22 12:55 AM

Hi,

 

ION9000T in a 230 IT system.

 

When not using a voltage transformer, (direct voltage connection to the meter) do I set: PT primary 1 and :PT secondary: 1  or PT primary: 230 /PT secondary: 230.

Thinking if there is any consequenses in the PQ reporting etc? 

 

 

BR 

GIA

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-02-22 08:03 AM

0 Likes
2
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-22 08:03 AM

Hello @geir_eas_no_bfo ,

 

Both ratios will work. You may get some warnings from ION Setup about Nominal voltage vs PT primary but these are just warnings.

 

Personally I prefer to use 230:230, this way it is always obvious to any user what the expected voltage of the system will be.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
geir_eas_no_bfo
Lt. Commander geir_eas_no_bfo
Lt. Commander

Posted: ‎2022-02-22 11:27 PM

0 Likes
1
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-22 11:27 PM

ok, tanx 🙂

 

btw: 

I`m not getting any "voltage spikes" on the ION9000T, ( could be a healty installation)  

Not sure if want to adjust Power Quality transient logging, other than default. But could this be related to the the waveform format? 

default it is 512x4. 

 

What do you recomend 1024x2 or 512x4 ?

 

sag/swell settings are learned limits: 110% / 98%

 

 

BR

GIA

 

Tags (2)
  • Tags:
  • english
  • ion9000
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-02-23 10:10 AM

0 Likes
0
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-02-23 10:10 AM

Hello @geir_eas_no_bfo ,

 

To start the ION9000 has 2 different transient detection, first is what the ION9000 (no T) has. This is configured with the Transient module linked to Waveform recorder modules. The second is a high speed transient (only on ION9000T), this is configured with the HSTC module and linked to HSTC waveform recorder modules.

 

Not seeing transients could be a health system or could be event priority is too low to generate an event, or could be module is disabled or settings are such that module is off line or settings ignore transient inside threshold. If you do not know know how to check these, please contact your local technical support.

 

The waveform recorder modules are independent to the module that triggers the waveform recorder. The format will have no baring on weather or not meter will trigger a waveform record pulse.

 

I cannot give a recommendation as it will always be dependent on end user needs. 1024x2 is highest sampling rate but short duration, 512x4 has longer duration but at a cost of less resolution.

 

Sag swell module and Transient modules are different modules and independent from each other.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of