ION9000 Big Reactive Power Difference

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Caglar_Abatay
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
12
1467

ION9000 Big Reactive Power Difference

Hello,

 

At our customer's facility there is a problem about Reactive Power Difference. 

I tried to draw a schema, you can see below.  Iskra and ION9000 use a common current transformer. 

 

What is your idea about this problem? Is there any setting about measurement format of ION9000 ?

ION9000 Reactive Power Difference.jpg

Tags (1)

Accepted Solutions
DanL
Commander Commander
Commander
4
1424

Re: ION9000 Big Reactive Power Difference

The "KVA tot Method" setup register does not affect nor configure the kVAR calculation method.

"KVA tot Method" only affects the "kVA tot" output of the power meter module and any calculation that depends on kVAtot (see ION Reference for more information)

 

It looks like there is no ION Setup wizard for disabling the "Use Fundamntal kVAR" method.

You will need to
1. select "Show Advanced ION Setup" in ION Setup's Device Properties window (see Tools tab),

2. navigate to the "Ext Bool Modules" and open ExtBool1 (UseFundkVAR).

3. SHIFT+click on the "Output Registers" tab to show the current configuration (default = true)

4. SHIFT+click on the output register "UseFundkVAR" and select "OFF"

5. SHIFT+click on the output register tab again to refresh (should now be false)

 
 

If you wish to implement some other method for computing kVAR (eg. Triangle method), you will need to create an Arithmetic module and configure it and link it as you wish.

See Answer In Context

Tags (1)
DanL
Commander Commander
Commander
0 Likes
1
1406

Re: ION9000 Big Reactive Power Difference

I am not at all surprised since the Quadrature method for computing VARs is quite different from the power triangle method with distorted or non linear loads.

Fortunately the equations for the power triangle method are clearly laid out in the whitepaper you linked and trivial to implement with an Arithmetic module.

Note: Be sure to set the KVA_tot method to "Arithmetic Sum" when using power triangle VARs, otherwise you will have a circular dependency.

 

I am curious what reason you might have for requiring this method? Is it purely for data consistency (with old meters)?

 

See Answer In Context

Tags (1)
12 Replies 12
Charles_Murison
Picard Picard
Picard
0 Likes
1
1463

Re: ION9000 Big Reactive Power Difference

Hello @Caglar_Abatay 

 

I would consider asking a question like this in the hardware section rather than PME in the future. I will see if I can get someone to help move it.

 

As to the question, I would ask the simple one first, what device do you trust more, how do you know that the ION9000 meter is not the correct reading? What do the phasor diagrams look like between the devices?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
DanL
Commander Commander
Commander

Re: ION9000 Big Reactive Power Difference

Differences in reactive power is usually due to harmonic content (often a non linear load) and different algorithms for measuring reactive power.

 

I'm guessing the "mW" and "mVAR" are intended to read "MW" and "MVAr" (Mega vs. milli prefix)?
If this is a milli-watt and milli-var load, this might be outside the nominal operational range of your meters (need to confirm PT and CT ratios).


Did you mean the "Iskra MC 350"? I cannot find information on a model "MC 35".
All the Iskra devices I found claim partial compliance to the legacy reactive energy spec: IEC62053-23 Class 2 (2%)

The IEC62053-23 standard only defines performance under sinusoidal steady state conditions, so that many different reactive power algorithms will comply to the mandatory tests (all tests are sinusoidal).

Iskra MC 350 specsIskra MC 350 specs

 

The ION9000 complies completely to this old standard and also to the new IEC62053-24 Class 0.5S (0.5%). The -24 standard enforces that reactive power be derived only from the fundamental component in the voltage and current signals.


My guess is that the PM870 is using the same/similar algorithm as the Iskra device.

Tags (1)
Caglar_Abatay
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1451

Re: ION9000 Big Reactive Power Difference

Hello @Charles_Murison ,

 

Yes I trust ION9000 but other two devices are measuring similar value. And difference is very big. I checked phasor diagrams  They look good.

 

Best Regards.

Tags (1)
Caglar_Abatay
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
8
1448

Re: ION9000 Big Reactive Power Difference

Hello @DanL 

 

You are right the device name is Iskra MC350.

 

I found a document about  reactive power calculation methods of Schneider analysors Last Year. "Calculation of Electrical Powers in Schneider Electric PMDs" I attached at this post. 

 

My first idea was to change reactive power calculation methods of ION9000. That's why I wrote this topic. But I will try your advices.

 

The main issue that confuses me is that the value read by the PM870 is very near to the value read by Iskra.

 

Best Regards.

Attachments
Tags (1)
DanL
Commander Commander
Commander
7
1435

Re: ION9000 Big Reactive Power Difference

I believe the PM870 used the "power triangle" method for reporting VARs.

 

The ION9000 computes two methods of VARs by default:

1) fundamental only (the default display value and default reactive energy method) always available on the Power Harmonics module outputs

2) "Quadrature method" always available on the Power Meter module outputs

 

Additionally, the ION9000 can be configured to compute other methods including the "power triangle" VAR quantity with an Arithmetic module.

Tags (1)
Caglar_Abatay
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
6
1430

Re: ION9000 Big Reactive Power Difference

Hello @DanL ,

 

You are right. How I change calculation method? I could not find in ION Setup.

 

Best Regards.

Tags (1)
Charles_Murison
Picard Picard
Picard
0 Likes
5
1427

Re: ION9000 Big Reactive Power Difference

Hello @Caglar_Abatay 

 

If you place the meter in advanced configuration, navigate to power meter modules -> Power meter. Under the setup registers there is KVA tot Method, Options are Vector Sum and Scalar Sum. Perhaps this will be able to do what you are looking for?

 

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
DanL
Commander Commander
Commander
4
1425

Re: ION9000 Big Reactive Power Difference

The "KVA tot Method" setup register does not affect nor configure the kVAR calculation method.

"KVA tot Method" only affects the "kVA tot" output of the power meter module and any calculation that depends on kVAtot (see ION Reference for more information)

 

It looks like there is no ION Setup wizard for disabling the "Use Fundamntal kVAR" method.

You will need to
1. select "Show Advanced ION Setup" in ION Setup's Device Properties window (see Tools tab),

2. navigate to the "Ext Bool Modules" and open ExtBool1 (UseFundkVAR).

3. SHIFT+click on the "Output Registers" tab to show the current configuration (default = true)

4. SHIFT+click on the output register "UseFundkVAR" and select "OFF"

5. SHIFT+click on the output register tab again to refresh (should now be false)

 
 

If you wish to implement some other method for computing kVAR (eg. Triangle method), you will need to create an Arithmetic module and configure it and link it as you wish.

Tags (1)
Caglar_Abatay
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
2
1410

Re: ION9000 Big Reactive Power Difference

Hello @DanL ,

 

I used Designer (PME) in order to this operation. I setted ExtBool1 (UseFundkVAR) to zero in designer. But there is a big difference at kVar values still.

 

I think so we need other method for computing kVAR. I will continue to research.

 

Thanks.

Tags (1)
DanL
Commander Commander
Commander
0 Likes
1
1407

Re: ION9000 Big Reactive Power Difference

I am not at all surprised since the Quadrature method for computing VARs is quite different from the power triangle method with distorted or non linear loads.

Fortunately the equations for the power triangle method are clearly laid out in the whitepaper you linked and trivial to implement with an Arithmetic module.

Note: Be sure to set the KVA_tot method to "Arithmetic Sum" when using power triangle VARs, otherwise you will have a circular dependency.

 

I am curious what reason you might have for requiring this method? Is it purely for data consistency (with old meters)?

 

Tags (1)
Caglar_Abatay
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1402

Re: ION9000 Big Reactive Power Difference

Hello @DanL 

 

Thank you for your answers and supports. 

 

Customer does not want this difference. That's all the reason.

Tags (1)
Caglar_Abatay
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
1335

Re: ION9000 Big Reactive Power Difference

Hello @DanL 

 

I created Triangle method in designer (PME). 

It seems to be working fine.
 
Thank you. 
Tags (1)