Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8650 Revunue meter Input Votage Reduce to 45V

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: ION8650 Revunue meter Input Votage Reduce to 45V
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
Pradip_SEL
Pradip_SEL Explorer
Explorer

Posted: ‎2015-09-24 04:06 AM

0 Likes
3
1325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-24 04:06 AM

ION8650 Revunue meter Input Votage Reduce to 45V

Dear All,

In one of our customer place(Power Plant) the meter measuring voltage reduce some time in a day around 45V(line to neutral).As per our ION8650 the measuring voltage specification

Input-voltage

characteristics (1)

Nominal voltage 57V to 277VLN rms

100V to 480VLL rms (35S)

Maximum voltage 347 VLN rms, 600 VLL rms (9S)

1)So in this case is it possible to measure the energy though ION8650 meter.

Tags (1)
  • Tags:
  • ion8650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Bojan
Bojan Leader
Leader

Posted: ‎2015-09-24 05:56 AM

0 Likes
2
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-24 05:56 AM

Hi Pradip,

I think that the input-voltage specifications are limited by the operating range of the power supply if a non-auxiliary power supply is used.

So, if the meter is externally-powered as Auxiliary Low Voltage Supply [65-120 VLN RMS (+-15%)@47-63Hz 80-160VDC(+-20%)] or Auxiliary High Power Voltage Supply [160-277VLN RMS (+=20%)@47-63HZ 200-350VD(+-20%)], it is possible to measure the energy though ION8650 meter.

Best Regards,

Bojan

Reply
Pradip_SEL
Pradip_SEL Explorer
Explorer

Posted: ‎2015-09-24 09:10 PM

0 Likes
1
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-24 09:10 PM

Dear Bojan,

I will manage to power up meter by supply external High power supply voltage.So meter will be on.But the measuring input voltage some time 45V(Line to neutral) in a day.So that time whether our meter is capable to measure energy below nominal voltage is 57V LN.

Pls suggest me.

Reply
Bojan
Bojan Leader
Leader

Posted: ‎2015-09-25 05:52 AM

0 Likes
0
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-09-25 05:52 AM

Hi Pradip,

My understanding is that the limitations, i.e. Standard 57-277 (+/-15%) VLN rms), are limited by the operating range of the power supply.

ION8600 Voltage Limitation.jpg

Best Regards,

Bojan

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore