Hello everyone,
I’m reaching out because we’ve encountered an issue with an ION8650 meter where the time has unexpectedly changed. Upon reviewing the event log, we noticed that this problem is related to the Sample TOU. However, the meter does not have any TOU configuration set up.
We’re concerned that this issue might happen again and would really appreciate any insights or suggestions you might have to help us understand and resolve it.
For your reference, I’ve attached the event log and the meter configuration report.
Thank you so much in advance for your support!
Best regards.
Link copied. Please paste this link to share this article on your social media post.
Hello @Veronika.Salinas ,
The TOU had nothing to do with the time change on the meter. If you look at the details, the time Change came from COM4, witch is set to ION protocol. Something or someone sent a time change to the meter via the Com4 Serial port.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Veronika.Salinas ,
The TOU had nothing to do with the time change on the meter. If you look at the details, the time Change came from COM4, witch is set to ION protocol. Something or someone sent a time change to the meter via the Com4 Serial port.
Regards,
Charles
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.