ION8650 Meter Load Profile Data Is Lagging

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650 Meter Load Profile Data Is Lagging
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
cchapman_AMP
Crewman cchapman_AMP
Crewman

Posted: ‎2024-08-16 07:00 AM

0 Likes
8
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-16 07:00 AM

ION8650 Meter Load Profile Data Is Lagging

I have an ION8650 that has a functioning and updated clock, but the Load Profile on the meter is lagging behind real time.  The data in the meter is 1.5 days behind real time.  Anyone ever seen this issue?

Labels
  • Labels:
  • ION Setup
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-08-22 02:17 PM

1 Like
0
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-22 02:17 PM

I strongly suggest to do the following if/when you observe a similar drift in the device in similar fashion:

1. Immediately connect to the device using ION Setup and observe the clock settings found in the ION Setup assistant.

Robert_Lee_0-1724361049634.png

Pay close attention to all of the Clock settings and what they are set to.  Whether you program Timezone or not should not matter unless you using time of use functionality as the ION meter operates in UTC.

Most applications need to realize that and interpret the data as such.  If for example the Time Sync Type is set to UTC but the time sync source were to sync using localtime, this would have an adverse effect on when daily operations might occur.

2. Download the exact same log using ION Setup and view the data side by side with PrimeRead.  Are they reporting similar values for the exact same date/timestamps?  Does ION Setup show the same inability to read the data (stays 12 hours behind for example) until the device is power cycled.




See Answer In Context

Reply
Replies 8
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-08-19 10:33 AM

0 Likes
1
1445
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 10:33 AM

Hi @cchapman_AMP 

 

Are you using ION Setup to check real time and Load Profile? If yes, please check Time Zone settings in ION Setup -> right click on the meter -> Properties -> Time Zone tab

 

If you are using PME, and a meter with a large amount of logged data which has recently started communicating with PME, it will take time for PME to catch up with all the logged data on the meter.

 

You can also check the amount of memory used to store Load Profile logs which depends on the number of parameters being logged and the frequency with which these parameters are logged.

 

In ION Setup, the Memory tab in the Logging folder of the Setup Assistant displays the memory
allocated to each log and the meter’s total in-use and available logging memory.

Mehran_Mehrnia_0-1724088046623.png

 

Best Regards,

-Mehran

L3 Expert tech Support Specialist

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-08-19 11:45 AM

0 Likes
1
1440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 11:45 AM

Hello @cchapman_AMP ,

 

Would you be able to give a few more details? For example how are you reading the timestamp for the Load profile, local time or UTC time? How is the clock on the meter set? How do you determine that data in the meter is behind real time?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
cchapman_AMP
Crewman cchapman_AMP
Crewman

Posted: ‎2024-08-19 11:59 AM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 11:59 AM

Hello, Charles,

 

The clock was showing the proper time.  This meter was set to DST=0 and the time on the clock was up-to-date to Eastern Time.  When checking the Load Profile log, the data showing in the meter was 27 hours behind the current time shown on the meter.  The logging memory was set to 35040 intervals.   Our PrimeRead application was calling and updating with the time and date found in the meter.

 

I was waiting for the owner of the meter to re-boot the meter and I was wondering what causes this issue and if there is a solution other than re-booting the meter.

 

On 8/18/2024, the owner re-booted the meter and it jumped the Load Profile to current date and time.   The jump in the meter skipped the 27 hours of data that we could see current the entire time in our SCADA connection to the solar field this meter resides in.

 

Luckily, I can use the SCADA data to correct the missing data in our PrimeRead system.

 

If you can share any insight into what may cause this in a meter, it would be appreciated.

 

Here are some details on the meter:

ION8650

Template is 8650B_V3.3.0.1.1

Revision (firmware) 004.020.001

 

Thank you.  Have a good day!

 

-Chris

Reply
cchapman_AMP
Crewman cchapman_AMP
Crewman

Posted: ‎2024-08-19 12:00 PM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-19 12:00 PM

Hello, Mehran,

 

Thank you for your response.  The Load Profile memory was 0.26% and Duration 260 and Records 6240.  Everything there looks normal.  Thank you again.  Have a good day!

 

-Chris

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-08-20 10:24 AM

0 Likes
1
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-20 10:24 AM

Not knowing precisely how PrimeRead is retrieving the Load Profile, I have a few questions.

1 If using ION Setup to read the exact same data, does ION Setup show the same date/timestamp for identical readings (i.e. ION Setup reports a reading having a value of X at date/time Y and PrimeRead is reporting the identical reading and timestamp).

2. The ION meter typically receives its time updates using UTC (Universal Coordinated Time) which is the time it is in Greenwich England without DST applied.  Since the TZOffset is 0, the meter will believe it is located there and all data records will reflect that same time.  PrimeRead should account for that (and use its own timezone to adjust for EST or EDT if preferred).

Confirm what other time sync setting are configured for and determine exactly what application is periodically updating the meter's time if necessary.

Robert_Lee_0-1724174524238.png


3. When the meter powered down/up was there a *gap* of data as shown when viewing by ION Setup (records just skipped ahead and there is missing 27 hours) or did it fill in missing data with zero values?  Or are you saying now ION Setup (and PrimeRead) are both showing the exact same data which is now complete and nothing is actually missing at all.




Reply
cchapman_AMP
Crewman cchapman_AMP
Crewman

Posted: ‎2024-08-21 06:11 AM

0 Likes
0
1341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-21 06:11 AM

Hello, Robert,

For the moment, we can ignore our PrimeRead system since it was acting normal.  Here is what was happening with meter.  Here is a simple example:  Let's say right now is 12noon EST January 1.  The on-meter load profile shows the last data for 6am EST January 1.  The meter, up to when it went down a week ago, was showing the on-meter load profile in synch with the current time.  There has been no time zones or time synchs or any changes.  At 5pm EST on January 1, the on-meter load profile is showing the last data as 11am EST January 1.  We re-booted the meter and then the issue has gone away but I wondered why this would happen?  The issue has been resolved.  My SCADA team was up-in-arms until I could get the team on-site to go re-boot it.  Thank you for your help and insight.  Have a good day!

 

-Chris 

 

Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-08-22 02:17 PM

1 Like
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-22 02:17 PM

I strongly suggest to do the following if/when you observe a similar drift in the device in similar fashion:

1. Immediately connect to the device using ION Setup and observe the clock settings found in the ION Setup assistant.

Robert_Lee_0-1724361049634.png

Pay close attention to all of the Clock settings and what they are set to.  Whether you program Timezone or not should not matter unless you using time of use functionality as the ION meter operates in UTC.

Most applications need to realize that and interpret the data as such.  If for example the Time Sync Type is set to UTC but the time sync source were to sync using localtime, this would have an adverse effect on when daily operations might occur.

2. Download the exact same log using ION Setup and view the data side by side with PrimeRead.  Are they reporting similar values for the exact same date/timestamps?  Does ION Setup show the same inability to read the data (stays 12 hours behind for example) until the device is power cycled.




Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-08-22 02:26 PM

1 Like
0
1334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-08-22 02:26 PM

You state in your first post:

Our PrimeRead application was calling and updating with the time and date found in the meter.

So depending on the CL1 TimeSync Type, if set to UTC, PrimeRead must properly set the time as GMT time (that in London without DST) and if the Timezone is set to Eastern Standard Time with no DST, then the CL1 LocalTime should show EST always (and never EDT).  If it is set to LocalTime, then the timezone must also be set properly as well as the ION meter will adjust the time sent via update to compute UTC.


Now, when retrieving the data log records, PrimeRead will need to interpret the date/timestamp for each record as UTC and adjust accordingly.


Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of