Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION8650 DNP Data Quality / Alarming

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION8650 DNP Data Quality / Alarming
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
sesa331493_brid
sesa331493_brid Leader
Leader

Posted: ‎2015-05-04 10:01 AM

0 Likes
1
1338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-04 10:01 AM

ION8650 DNP Data Quality / Alarming

I am trying to fulfill a requirement to get our ION 8650 Meter certified to use as a RIG on the CAISO control grid. I am running into a stumbling block on determining if our meter has sufficient DNP Quality and alarming.  Here is the requirement.

The RIG/DPG shall be able to send CAISO a data quality indication. The RIG/DPG shall provide a DNP ONLINE / OFFLINE quality flag on a per point basis. CAISO will fail and re-establish the communication to the external device.

The use of DNP ONLINE / OFFLINE quality flag is required for all analog points. When communication is lost with any external device the analog data associated with that device should indicate an OFFLINE status. The use of the DNP ONLINE / OFFLINE quality flag shall be set from within the RIG/DPG.

For example:

If there are two serial communication ports ‘A’ and ‘B’ connected to the RIG/DPG device and port ‘A’ fails, those points associated with port ‘A’ alone have their DNP data quality flags set to OFFLINE internally to the RIG/DPG. While port ‘B’ data points DNP remain set to ONLINE.

If external points are connected to a network LAN device and the LAN fails to communicate only those points associated to that LAN port have their DNP quality flags set to OFFLINE

I am not sure if the ION8650’s DNP modules are already designed to do this or if it would require modification. Most of the data coming into the meter will be modbus data coming in on the Ethernet, the meter being a Modbus master to several slave devices. The data will then be exported out of the meter through DNP. If one of the slave devices looses communication there needs to be a quality flag for that group of DNP values showing it as bad quality or Offline. The rest of the values need to stay online. 

Tags (3)
  • Tags:
  • dnp
  • dnp3
  • ion8650
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
sesa44646
sesa44646 Leader
Leader

Posted: ‎2015-05-04 12:45 PM

0 Likes
0
1300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-04 12:45 PM

Hi Matthew - Moving this to Hardware community so it will get noticed.

- Vince

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore