Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PQ measurements with ION 7650 in a 3W Delta System

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PQ measurements with ION 7650 in a 3W Delta System
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
ekourany_btupan
ekourany_btupan
Troubleshooter

Posted: ‎2015-05-01 08:21 AM

0 Likes
2
2003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-01 08:21 AM

PQ measurements with ION 7650 in a 3W Delta System

Hi Guys..

I have an application for power and quality monitoring in a Data Center.. However, the data center power system configuration is Delta 3W ungrounded.. The meter to be used is an ION 7650 with 3-Wire Delta, 2½-Element, Direct Connection (VOLTS MODE = Delta)

My concern is that sag & swell as well as transient detection functionality is based on the line to neutral voltage reference.. I am a bit puzzled as to what would be the correct voltage reference to provide on the NOM VOLTS configuration parameter that is required to input  in order to activate this detection functions within the meter.. and secondly, but most importantly how to interpret the meter sags and swell, and transient captured data.. i.e. power quality reports/ CBEMA curves in the context of an ungrounded system, etc..

I wonder if you can share some light and "heads up" into this particular application and perhaps share some tech-notes that explain in bit more detail how the meter sags & swell and transients frameworks work. This would be very valuable in the hopes to give the end user / customer a better understanding of his particular setup and what type of data/information to expect from implementing PQ analyzer within their facility with ION 7650 meters.

Thanks for your prompt comments and guidance.

Tags (5)
  • Tags:
  • 3w
  • 7650
  • a
  • delta
  • in
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
sesa56307_bridg
sesa56307_bridg Troubleshooter
Troubleshooter

Posted: ‎2015-05-01 09:56 AM

0 Likes
1
1945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-01 09:56 AM

I don't have a deep expertise in Delta 3W ungrounded systems (I'm others can provide more detailed insight there).  However, I do know that the Sag/Swell and Transient features on the ION7650 are designed to work properly with a line-to-line voltage reference in Delta mode.  The associated ION modules use a nominal voltage setting that is interpreted as a line-to-neutral value for Wye systems, or a line-to-line value for Delta systems.  So the nominal voltage value should be interpreted correctly in both cases.  And the resulting calculation outputs are definitely based on line-to-line values for Delta systems.

I suggest the ION Reference document as a good place to start for a full understanding of the Sag/Swell and Transient modules.  Here are a couple of excerpts.

Description of the "Nom Volts" setup register on the Sag/Swell module:

6337

Description of the "Nominal" input on the Transient module (which is typically linked to the Sag/Swell Nom Volts setup register by default):

6338

Reply
ekourany_btupan
ekourany_btupan
Troubleshooter

Posted: ‎2015-05-01 10:49 AM

0 Likes
0
1945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-01 10:49 AM

Thanks David. That was very helpfull.

Indeed after reviewing the latest ION Reference manual it is clear that the ION7650 are designed to work properly with a line-to-line voltage reference in Delta mode, and that the NOM VOLT setup register should be fed with the line to neutral or line to line voltage values depending on power system configuration.

I guess the down fall for the delta configuration, from what I have found so far, is that Line to ground disturbances however, can´t be monitored with the meter when the power system is Delta ungrounded and the meter is wired and configured with as DELTA 3W system.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore