Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

ION7650 Which nominal voltage?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7650 Which nominal voltage?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
525
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2015-01-22 02:08 AM

0 Likes
3
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-22 02:08 AM

ION7650 Which nominal voltage?

Which nominal voltage should I use for this network (4W-WYE) so that the ION7650 takes waveforms? (15400.00V or 8891.19V ?)

(There is no real neutral conductor in the medium voltage station.)

5606

Is it enough to fill in the nominal voltage for getting waveforms, or do I still need to configure something else?

Tags (7)
  • Tags:
  • ion7650
  • mode
  • nominal
  • pme
  • voltage
  • volts
  • waveforms
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2015-01-23 06:31 AM

0 Likes
0
1578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-23 06:31 AM

Hi Christine,

I think Philippe is asking about nominal voltage from Basic Setup, not Sag / Swell Module Settings - Nominal Voltage from Basic Setup is for harmonics calculation, and Nom Volts from Sag / Swell Module Settings is used for all Power Quality functions.

According to ION7650 / 7550 Programming Guide Nom Volts from Sag / Swell Module Settings is the primary power system voltage (sometimes different than PT Primary setup register value), which should be the same as Nominal Voltage from Basic Setup, I guess.

Best Regards,

Bojan

See Answer In Context

Reply
Replies 3
sesa70148
sesa70148 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-01-22 04:38 PM

0 Likes
2
1578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-22 04:38 PM

Hi Philippe, you might need to set the nominal voltage for Sag/Swells in order for the meter to capture waveforms. I know this setting impacts a lot of the power quality features. You can do this in the ION Setup Assistant, on the Power Quality > Sag/Swell screen. There should be a setting for nominal voltage.

Reply
Hal_Etheridge
Janeway Hal_Etheridge Janeway
Janeway

Posted: ‎2015-01-22 04:49 PM

0 Likes
0
1578
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-22 04:49 PM

The nominal voltage setting is required by the Sag/Swell module to correctly trigger waveforms *through that module*.  The nominal voltage should not need to be set to capture waveforms in general.  For instance you can manually trigger a waveform capture without setting this value.  What setting the nominal value does is configuring the Sag/Swell module thresholds as to what is a Sag or Swell.  No setting means no Sag or Swells will be detected and thus no waveforms will be automatically triggered in that particular situation as a side effect.

For the question whether the nominal voltage you need to program is the primary or secondary voltage I am not sure.

Reply
Bojan
Admiral Bojan Admiral
Admiral

Posted: ‎2015-01-23 06:31 AM

0 Likes
0
1579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-01-23 06:31 AM

Hi Christine,

I think Philippe is asking about nominal voltage from Basic Setup, not Sag / Swell Module Settings - Nominal Voltage from Basic Setup is for harmonics calculation, and Nom Volts from Sag / Swell Module Settings is used for all Power Quality functions.

According to ION7650 / 7550 Programming Guide Nom Volts from Sag / Swell Module Settings is the primary power system voltage (sometimes different than PT Primary setup register value), which should be the same as Nominal Voltage from Basic Setup, I guess.

Best Regards,

Bojan

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore