Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
Hi All,
Questions on ION7350 harmonics. How does the 31st harmonics calculated (or if it is measured) given that it is supplied via CT's?Is the value calculated or measured?
Any idea would help
Thanks
Evonne
Link copied. Please paste this link to share this article on your social media post.
On the ION7350, an FFT calculation is done at 64 samples per cycle on a measured waveform to produce harmonic readings from the 2nd to 31st.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.