ION Setup and iEM3155/3255 problem
Metering & Power Quality
Select a Country
  • EcoStruxure Power & Grid
  • ION Setup and iEM3155/3255 problem
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
sesa8515
sesa8515 Leader
Leader
Posted: ‎2013-03-07 02:20 AM . Last Modified: ‎2020-04-22 01:55 AM
2124
Here is feedback from customer that is using ION Setup to configure iEM3xxx meters:
- ION setup shows energy in W but in description is kW
- after saving project with iEM3xxx meters the polarity setting (like 8N1) is lost
- there is not energy divided by tariffs visible in ION Setup when using iEM3155 (device is correctly added as "A9MEM3155" in Template Options)
- there is not tariff setting when using iEM3155 (device is correctly added as "A9MEM3155" in Template Options)
ION Setup version used: 3.0.12242.01
  • ION Setup
Tags (3)
  • iem3000
  • ion
  • setup
Robert_Lee
Robert_Lee Champion
Champion
Posted: ‎2013-03-08 09:02 AM
1995
Thanks Jan for forwarding the feedback.
I'll modify the energy display to divide the registers to correctly display the readings in kW (i.e. 1234 watts will now be shown as 1.234 kW).  As for the tariff information not being shown, I'm waiting on marketing to correctly identify what information they would want ION Setup to display from this device as a viewing tool before going ahead and designing supporting table view displays.  If you could provide some guidance, that would be helpful as well.
Robert_Lee
Robert_Lee Champion
Champion
1996
sesa8515
sesa8515 Leader
Leader
Posted: ‎2013-03-12 09:12 AM
1995
Hello Robert,
if you choose this type of meter:
1164
there should be possible to set up tarrif:
1156
Regards
Jan
Robert_Lee
Robert_Lee Champion
Champion
Posted: ‎2013-03-15 11:50 AM
Hi Jan,
     It looks like the documentation is incorrect in listing that Multi-Tariff mode command is available.  I've discussed this with the iEM3000 developer in Shanghai and he's indicated that the Multi-Tariff mode can be only modified via the front panel HMI in the present firmware.
I've also modified the setup files to show the energy values in the correct units now (i.e. 123456 watts will be shown as kW 123.456) so if you need to know how to do this immediately, just send me an e-mail (robert.lee@ca.schneider-electric.com) and I'll send you the instructions how to fix it.