ION 9000 used as gateway

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 9000 used as gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
525
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
mickkennedy
Ensign mickkennedy Ensign
Ensign

Posted: ‎2025-03-11 08:22 AM

0 Likes
5
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-11 08:22 AM

ION 9000 used as gateway

Hi,

 

I'm trying to use an ION9000 as a gateway to 5 x sepam protection relay on serial line.

 

Communication is possible but performance is really poor.

 

ION is setup correctly to align with Slave devices re:baud/parity etc.

 

meter is setup correctly to act as a gateway in the advance section of IONsetup->modbus master module options etc.

 

my question is - is the comms performance of the ION 9000, acting as a gateway, known to be limited or poor? Is it poor in this case because of the fact that it is trying to allow 5 x SEPAM to communicate through it, would it perform better if the slave devices were a more basic  equipment?

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-03-12 01:04 AM

0 Likes
1
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-12 01:04 AM

Hi @RobGraham , 

 

Original thread here:

https://community.se.com/t5/Gateways-and-Energy-Servers/ION9000-used-as-a-gateway/td-p/503186

 

Last answer from Mick:

"5 x SEPAM have ACE949-2 interface each.

I'm reviewing the 'Time util%' and ''Avg request ratios' in Diagnostic viewer to measure Comms performance.

not sure exactly what you mean by your next question - "What kind of Master is connected upstream you ION9000" . the ION9000 is connected as an ethernet device and configured as a gateway to the SEPAMs"

 

@mickkennedy 

My question was about the type of system connected to your ION9000. Now I have my answer: you are connected to PME. 

 

PME is not very stressful with Sepam, because not so much requests are sent by PME to the Sepam.

I do not expect "high comm performances" for this kind of connection because ACE949 translates Sepam protocol to RS485. ION9000 translates Modbus RS485 to Modbus TCP. And you have a daisy chain of 5 ACE949-2.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 5
RobGraham
Commander RobGraham Commander
Commander

Posted: ‎2025-03-11 09:05 AM

0 Likes
2
1118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-11 09:05 AM

I haven't seen any issues with using the ION9000 as a gateway, myself.  How are you defining "poor performance"?  Are you receiving exception codes?  Gateway timeouts?  Other?

 

Also, what software are you using to communicate to the daisy chain?  Serial communications are extremely fickle.

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-03-12 01:04 AM

0 Likes
1
1090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-12 01:04 AM

Hi @RobGraham , 

 

Original thread here:

https://community.se.com/t5/Gateways-and-Energy-Servers/ION9000-used-as-a-gateway/td-p/503186

 

Last answer from Mick:

"5 x SEPAM have ACE949-2 interface each.

I'm reviewing the 'Time util%' and ''Avg request ratios' in Diagnostic viewer to measure Comms performance.

not sure exactly what you mean by your next question - "What kind of Master is connected upstream you ION9000" . the ION9000 is connected as an ethernet device and configured as a gateway to the SEPAMs"

 

@mickkennedy 

My question was about the type of system connected to your ION9000. Now I have my answer: you are connected to PME. 

 

PME is not very stressful with Sepam, because not so much requests are sent by PME to the Sepam.

I do not expect "high comm performances" for this kind of connection because ACE949 translates Sepam protocol to RS485. ION9000 translates Modbus RS485 to Modbus TCP. And you have a daisy chain of 5 ACE949-2.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
RobGraham
Commander RobGraham Commander
Commander

Posted: ‎2025-03-12 05:36 AM

1 Like
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-12 05:36 AM

Thank you!  I agree that 5x Sepam relays should not be a problem, so my next question is, are there any other clients connected to the daisy chain (EPO, PLCs, BMS, etc.)? 

 

You may also be able to increase the baud rate to improve performance.

Reply
mickkennedy
Ensign mickkennedy Ensign
Ensign

Posted: ‎2025-03-12 08:46 AM

0 Likes
1
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-12 08:46 AM

Thanks @RobGraham 

 

When i say 'poor performance' i mean high %value in 'time util%' section of diagnostic viewer and 'avg request ratios' higher than ideal  at 4 or 5.##

 

Also and most significantly the graphic on webview is slow to update and does loose comms frequently.

 

performance is ok with one SEPAM, but gets worse as i add/enable more devices

 

As experiment i put the serial line through a spare link 150 i had with immediately better results and have had no comms issues now for 2 or 3 days. all the figures i referred to above from diagnostic viewer look way healthier.

 

i dont have any software on the server like modscan or modbus poll to see if i am getting any exceptions.

 

thanks for help with this, open to any more education on how to analyse the issue

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-03-12 10:12 AM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-12 10:12 AM

Hello @mickkennedy ,

 

If you want to do a really deep dive, would recommend getting some kind of serial analyzer tools such as IFTtools RS-485 analyzer (https://www.iftools.com/analyzer/index.en.php). This way you could see what is using up so much of the bandwidth. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore