ION 9000 harmonics

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 9000 harmonics
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
520
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
132
Ramasamy_N
Captain Ramasamy_N Captain
115
Robert_Lee
Admiral Robert_Lee Admiral
96
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
jerry_IPACS
Lieutenant JG jerry_IPACS
Lieutenant JG

Posted: ‎2020-02-13 08:56 PM

0 Likes
4
2439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-13 08:56 PM

ION 9000 harmonics

Hi everyone, 

 

I am having some difficulty in obtaining some harmonics measurements from the ION 9000 meters. The ION 9000 in question are all in DEMO mode. The meters are not recording anything for Voltage/Current THD and K-factor mean values, whereas they record zero for Voltage/Current THD and K-Factor High values. I have attached a Power Monitoring Expert Vista diagram that shows the problem. I have enabled IEEE 519 Harmonics Monitoring and EN50160 Power Quality Monitoring. There is also a PM8000 meter logging data accurately - all harmonics are being logged (this meter is also in DEMO mode). Is the issue due to some setup configuration in Power Monitoring Expert, or the meter itself? Does the ION 9000 have any issues like this because of DEMO mode? Any insight would be appreciated. 

 

Thanks, 

Jerry 

 

@Grant_IPACS 

 

Jerry Benny - IPACS Group
Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2020-02-18 03:46 PM

0 Likes
0
2425
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-18 03:46 PM

Harmonics (among many other PQ features) are not really implemented for DEMO mode. If I remember correctly, the harmonics related modules revert to 4WYE mode if volts-mode is set to DEMO (ie. they measure the signal on the inputs).
Since distortion is usually measured as a ratio (% of fundamental, or % of 'MaxDemand'), the divide by zero with no signal connected will result in the report showing "N/A" data.

See Answer In Context

Reply
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-14 09:29 AM

0 Likes
1
2436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-14 09:29 AM

Hello Jerry,

 

I would work backwards for something like this. I will assume that PME is able to upload any logs on the device (can be configured to skip certain recorders is configured to do so (very unlikely but something to check). 

First does the meter have Harm mean Log data recorder module?
Is the module enabled, is module online? (ION Setup will show red X on modules offline) External Boolean Harm Log Enable for enable on my meter.

Does the module have inputs linked?
Do the inputs have N/A? 

 

In ION Setup, go to advanced mode and connect to the data recorder. At the output tab, Hold <crtl> and left click the "Harm mean log" -> Read Value.

Select a range that will return 15 or less records, for example 1855 to 1864. (Actual values will depend on where the meter log position is at)
If you get results then the issue is likely not with the Meter but with PME getting the data into the data which is a very different problem.

L4 Prime for Advanced metering and Utilities
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2020-02-14 11:45 AM

0 Likes
0
2433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-14 11:45 AM

Hello

 

Found a meter that I can put in demo mode. If you trace inputs to the THD measurement you will find an Arithmetic module where inputs are 0 but calculation is S1/S2 for example, device by 0 results in N/A so data recorder has nothing to log.

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2020-02-18 03:46 PM

0 Likes
0
2426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-18 03:46 PM

Harmonics (among many other PQ features) are not really implemented for DEMO mode. If I remember correctly, the harmonics related modules revert to 4WYE mode if volts-mode is set to DEMO (ie. they measure the signal on the inputs).
Since distortion is usually measured as a ratio (% of fundamental, or % of 'MaxDemand'), the divide by zero with no signal connected will result in the report showing "N/A" data.

Reply
Yut
Captain Yut
Captain

Posted: ‎2020-02-18 09:03 PM

0 Likes
0
2424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-18 09:03 PM

Just connect AC supply to all Voltage input then use mode 4WY the PT ratio is 1 (as default).

Demo mode will not give harmonics value.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore