Hello Experts,
Please how do I configure an ION7650 to trip a CB at the threshold of Power rating?
At a certain threshold I desire the ION7650 to send a trip signal to open a Circuit Breaker.
Also I need the latest version of the ion setup software.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Q1 & Q2. How do I configure an ION7650 to trip a CB at the threshold of Power rating? At a certain threshold I desire the ION7650 to send a trip signal to open a Circuit Breaker.
>> Please follow the below steps;
I have created similar functionality for kVA. Please see below the screen shots for your reference.
Q3. Also I need the latest version of the ion setup software.
>> Please download it from the below web link. You may have to create your login.
Link copied. Please paste this link to share this article on your social media post.
Q1 & Q2. How do I configure an ION7650 to trip a CB at the threshold of Power rating? At a certain threshold I desire the ION7650 to send a trip signal to open a Circuit Breaker.
>> Please follow the below steps;
I have created similar functionality for kVA. Please see below the screen shots for your reference.
Q3. Also I need the latest version of the ion setup software.
>> Please download it from the below web link. You may have to create your login.
Link copied. Please paste this link to share this article on your social media post.
If you would like more information on the Setpoint module and its settings, it is described in the ION Reference. You can download the ION Reference from the following link:
Link copied. Please paste this link to share this article on your social media post.
You can get the latest version of ION Setup from the following link on Box:
https://schneider-electric.app.box.com/ionsetuplatest
If you are still working on Windows XP, we make a version for now that still works on that operating system:
https://schneider-electric.app.box.com/ionsetupforXP
Since ION Setup is constantly being updated, it isn't practically to keep updating the ones located on the standard =S= or PowerLogic web sites by myself.