Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to calculate demand for pulses on a DI of an ION7650?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to calculate demand for pulses on a DI of an ION7650?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Philippe_Morel
Philippe_Morel Mentor
Mentor

Posted: ‎2015-03-13 02:40 AM

0 Likes
3
1899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-13 02:40 AM

How to calculate demand for pulses on a DI of an ION7650?

How to calculate last demand and predicted demand for pulses on a digital input of an ION7650?

This is done automatically with a PM800 and a PM5561. (INPUT METERING)

Can an ION7650 also do this? Which modules should I use in Designer?

Tags (4)
  • Tags:
  • demand
  • ion7650
  • pulse
  • wages
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2015-03-15 06:37 PM

1 Like
0
1830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-15 06:37 PM

Most likely you can do the differential calculation in the arithmetic module, possibly in combination with some other modules like the store module (to keep the previous interval's ending value for instance) or just use the ART module's capability of keeping previous calculated values.

Another option is to convert the incoming pulses into the current demand value and then use the normal demand modules to calculate the interval demand values.  This seems to be the ION equivalent of the method described for the 820MG above.  Maybe something like a counter module to count the cumulative pulses per interval and then converting that into a power using an ART module and linking that to a demand module.  Just a guess though.

There is almost always multiple methods to solve a given problem with various combinations of ION modules.  I would suggest just breaking the problem down into a series of small calculation steps and then convert those into a set of ION modules.  Once you have a working solution then that can be applied to any ION device.

See Answer In Context

Reply
Replies 3
Mitun_Paul
Mitun_Paul Troubleshooter
Troubleshooter

Posted: ‎2015-03-13 10:18 AM

0 Likes
2
1830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-13 10:18 AM

Hi Philippe,

Could you please elaborate your question. What do you mean by demand for pulses? It would be great if you explain with some example.

Reply
Philippe_Morel
Philippe_Morel Mentor
Mentor

Posted: ‎2015-03-15 04:22 AM

1 Like
1
1829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-15 04:22 AM

Hi Mitun,

Below you'll find an extract from the manual of the PM820MG.

5945

The same for the PM5500.

5947

I think I found how to program Last Completed Interval Demand in Designer.

But I can't program the Partial Interval Demand.

Below you'll find an extract from the register list of the METSIM10M.

Here you also have the "instantaneous values" (calculated with the pulses on a digital input). This is what I really want.

But I think the ION7650 needs therefore a differential module (the opposite of the integrator module).


5946

Reply
Hal_Etheridge
Hal_Etheridge Champion
Champion

Posted: ‎2015-03-15 06:37 PM

1 Like
0
1830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-03-15 06:37 PM

Most likely you can do the differential calculation in the arithmetic module, possibly in combination with some other modules like the store module (to keep the previous interval's ending value for instance) or just use the ART module's capability of keeping previous calculated values.

Another option is to convert the incoming pulses into the current demand value and then use the normal demand modules to calculate the interval demand values.  This seems to be the ION equivalent of the method described for the 820MG above.  Maybe something like a counter module to count the cumulative pulses per interval and then converting that into a power using an ART module and linking that to a demand module.  Just a guess though.

There is almost always multiple methods to solve a given problem with various combinations of ION modules.  I would suggest just breaking the problem down into a series of small calculation steps and then convert those into a set of ION modules.  Once you have a working solution then that can be applied to any ION device.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore