Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION 75/650's Current Inputs with 1A or 1V

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 75/650's Current Inputs with 1A or 1V
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
JamesAZZO
JamesAZZO
Leader

Posted: ‎2015-10-13 01:05 AM

0 Likes
3
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-13 01:05 AM

ION 75/650's Current Inputs with 1A or 1V

We have a situation in a utility substation with CT’s ratios of 600:1A but the overcurrent max CT ratings are 1250A on the high side so we are looking just over 2A for the max current at the meter. I’m assuming we should be ordering the 1A calibration for the 1A CTs and that if it overruns the 1A (up to 2A n this case) that the meter will handle that as the inputs appear to be capable of up to 10A with this calibration.

Also, I would like confirmation that we can order the ION 7650 with Current Probe (Voltage) inputs 1V? Now, the real question is, can we use 1/3V / 0.333V CTs with this input order option? I was told yes once but I don’t know if I was understood since it’s not a 1/3V meter, but can I set the nominal to 0-.333?

John Straughn / James Clark?

Tags (4)
  • Tags:
  • 7550
  • 7650
  • calibration
  • current
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa50168
sesa50168 Leader
Leader

Posted: ‎2015-10-13 03:47 PM

0 Likes
1
1972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-13 03:47 PM

Hi James -

Regarding the  600:1A CT question, the key point is the accuracy range of the current inputs of the meter.  The accuracy range for the Class 20 inputs, which is the typical range ordered for a 5A CT, is 50mA to 20A. The Class 2 input range supports 1A, 2A, 5A and/or 10A nominal inputs.  The accuracy range is from 10mA to 10A.  Therefore even if your 1A CT is generating a 2A output, the meter can handle it.  The correct order option is the 1A CT input, so that the meter will be calibrated for the potential lower range of current input associated with a 1A CT.

I confirm that the meter can be ordered to accept 0-1V current probe inputs.  I will advise separately regarding the compatibility with .333V CTs.

See Answer In Context

Reply
Replies 3
sesa50168
sesa50168 Leader
Leader

Posted: ‎2015-10-13 03:47 PM

0 Likes
1
1972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-10-13 03:47 PM

Hi James -

Regarding the  600:1A CT question, the key point is the accuracy range of the current inputs of the meter.  The accuracy range for the Class 20 inputs, which is the typical range ordered for a 5A CT, is 50mA to 20A. The Class 2 input range supports 1A, 2A, 5A and/or 10A nominal inputs.  The accuracy range is from 10mA to 10A.  Therefore even if your 1A CT is generating a 2A output, the meter can handle it.  The correct order option is the 1A CT input, so that the meter will be calibrated for the potential lower range of current input associated with a 1A CT.

I confirm that the meter can be ordered to accept 0-1V current probe inputs.  I will advise separately regarding the compatibility with .333V CTs.

Reply
JamesAZZO
JamesAZZO
Leader

Posted: ‎2015-11-17 08:14 PM

0 Likes
0
1972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-17 08:14 PM

John - I need to know that answer about the .333V CTs if it supports 1V CTs.

Reply
Yut
Yut
Leader

Posted: ‎2015-11-18 11:43 PM

0 Likes
0
1972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-11-18 11:43 PM

If the meter is  5A option you should not have any problem install it into 1A  CTs, many time we install the ION7550/7650  5A meter with 1A CT they pass the test at site easily try it.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore