Hi
I want to know during the period we set, will Vigilohm continuously showing the measurement on display?
Thanks
Posted: 2015-10-28 07:54 AM
Link copied. Please paste this link to share this article on your social media post.
Hello Abon chen,
I am not quite clear about your question, what period do you mean?
Posted: 2015-10-28 07:54 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2015-10-28 05:51 PM
Link copied. Please paste this link to share this article on your social media post.
The time delay period.
Posted: 2015-11-01 10:31 PM
Link copied. Please paste this link to share this article on your social media post.
I found that the Power Circuit mode in IM400 is what I need for the high disturbed environment caused by frequent start-up of VSDs.
By injecting low frequency current, IM400 can measure w/o being biased by capacitive loads.
However, if there is high frequency current in the environment, will IM400 be affected?
Posted: 2015-11-05 06:02 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Abon Chen,
1. yes, power circuit mode is used to avoid frequency disturbances.
2. IM400 inject low frequency signal, will not be affected by high frequency current.
Posted: 2015-11-17 12:34 AM
Link copied. Please paste this link to share this article on your social media post.
Hi CHEN,
May I know if I can use IM400 with generators? I only see IM400 installed under transformer, not sure it can be applied with generators.
Thanks
Abon
Posted: 2015-11-17 11:59 PM
Link copied. Please paste this link to share this article on your social media post.
please make sure it is IT system.