The size of each record of a WaveForm Recorder module as stored in the ION7400 flash ranges from approximately 2kB to 8.5kB depending on the "Format". Most formats are between 7kB and 8kB.
The total size of a WaveForm Recorder module as stored in the ION7400 flash can be approximated Record size x "Depth".
The total size per module may not exceed 10MB (max Depth is about 1200 to 5200 depending on configured format)
Link copied. Please paste this link to share this article on your social media post.
The size of each record of a WaveForm Recorder module as stored in the ION7400 flash ranges from approximately 2kB to 8.5kB depending on the "Format". Most formats are between 7kB and 8kB.
The total size of a WaveForm Recorder module as stored in the ION7400 flash can be approximated Record size x "Depth".
The total size per module may not exceed 10MB (max Depth is about 1200 to 5200 depending on configured format)
Link copied. Please paste this link to share this article on your social media post.
Hello @Veronika1 ,
Context behind question?
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Charles_Murison
A customer wanted to know this in order to define the capacity of a new storage disk. Their system requires an important number of waveform captures.
Regards.
Link copied. Please paste this link to share this article on your social media post.
In that case, please disregard my above answer to a completely different question.
You are concerned about some software system (PME? what version?) and database system impact on capacity, and not the ION7400 capacity.
Link copied. Please paste this link to share this article on your social media post.
Hello @Veronika1 ,
While you can use Dan's post as a guide, note that PME will store waveform data in the same database as logging and event records. Therefore, a much more complex question than simply how much data per waveform.
For greater details recommend reaching out to technical support. The link https://digital-energy-help.se.com/pme/content/8_reference/planning/ref_dbgrowth.htm could be of some help.
Regards,