Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Power Tag Rope (A9MEM1591) installation

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Power Tag Rope (A9MEM1591) installation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Christian_Sáenz
Christian_Sáenz Contributor
Contributor

Posted: ‎2022-12-13 08:30 PM

1 Like
2
2791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 08:30 PM

Power Tag Rope (A9MEM1591) installation

Hi team;

 

SI said:

"In the installation manual it appears that the sensor loop must be fixed to the cable where it is going to be measured (as shown in the figure), but when we try to place it, there is no space to fix it (it remains as in the attached image).
What could we do in this case? Is it possible that it remains unfixed? Do you take the correct measurement?"

Christian_Senz_0-1670992211201.png

 

Christian_Senz_1-1670992054319.png

Please, thanks!

BR

 

CS

Labels
  • Labels:
  • PowerTag Energy
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Thierry_Baudard Champion
Champion

Posted: ‎2022-12-13 10:35 PM

0 Likes
0
2782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 10:35 PM

Hello Christian,

 

concerning installation:
Fix the cable make sense when the installation offer the possibility to do it but as you mention, it is not always possible.
The main objective of the installation is to minimize the influence of the two surrounding phases to the Rogowski loop of the measured one.
For this, two advices for your installation:
1) Check that the wires between the sensors and the PowerTag module are not in direct contact with one of the three measured phase conductor (picture1, extract from the instruction sheet)
2) Install the connection box of Rogowski loops for phase X and Z on the left and right sides and not in the middle to not be close to the conductor of the 2nd phase. (picture2)

 

Concerning accuracy :
Of course, the best accuracy for the current measurement is obtained with a conductor perfectly centered in the loop and perpandiculaire to this one. In this case accuracy will be very good and really better than 1%/class1 …but this setup can be created in laboratory and cannot not be reproduced easely in real and industrial use case.
So obviously, whatever the position of the cable in the loop, whatever the angle between the loop and the phase cable, "only" accuracy 1%/class1 according to standard IEC61557-12 is garranted by Schneider Electric

Picture1.jpgPicture2.jpg

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Reply
Replies 2
Thierry_Baudard
Thierry_Baudard Champion
Champion

Posted: ‎2022-12-13 10:35 PM

0 Likes
0
2782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-13 10:35 PM

Hello Christian,

 

concerning installation:
Fix the cable make sense when the installation offer the possibility to do it but as you mention, it is not always possible.
The main objective of the installation is to minimize the influence of the two surrounding phases to the Rogowski loop of the measured one.
For this, two advices for your installation:
1) Check that the wires between the sensors and the PowerTag module are not in direct contact with one of the three measured phase conductor (picture1, extract from the instruction sheet)
2) Install the connection box of Rogowski loops for phase X and Z on the left and right sides and not in the middle to not be close to the conductor of the 2nd phase. (picture2)

 

Concerning accuracy :
Of course, the best accuracy for the current measurement is obtained with a conductor perfectly centered in the loop and perpandiculaire to this one. In this case accuracy will be very good and really better than 1%/class1 …but this setup can be created in laboratory and cannot not be reproduced easely in real and industrial use case.
So obviously, whatever the position of the cable in the loop, whatever the angle between the loop and the phase cable, "only" accuracy 1%/class1 according to standard IEC61557-12 is garranted by Schneider Electric

Picture1.jpgPicture2.jpg

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
Christian_Sáenz
Christian_Sáenz Contributor
Contributor

Posted: ‎2022-12-14 02:43 PM

0 Likes
0
2774
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-12-14 02:43 PM

Thanks @Thierry_Baudard !

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore