IEM3255 and KepServer EX setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • IEM3255 and KepServer EX setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
ChickenRich
Crewman ChickenRich
Crewman

Posted: ‎2024-11-01 01:48 AM

0 Likes
6
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-01 01:48 AM

IEM3255 and KepServer EX setup

Hi, has anyone had an issue with setting up KepserverEX to read the Modbus kWh address 45100 which is a 32bit float on a IEM3255 energy meter?  KepserverEX reads all the other registers such as Voltage & Current registers which are also 32bit float and returns the correct values.  It won't read the kWh value and just returns a Zero.  I've tried other SCADA platforms such as Ignition and this reads it fine. Any help appreciated

Labels
  • Labels:
  • iEM3000
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-11-07 09:56 AM . Last Modified: ‎2024-11-07 10:12 AM

0 Likes
1
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 09:56 AM

Most present Schneider documentation states the Modbus address using standard Modbus Power Data Model (PDM) addressing.  In some instances, products may be published using PDU addressing (which is the address sent over communication to the actual device).

Now, I don't know how Kepware wants the address to be entered via its UI.  I would not think it would want to have users enter in Data Model addressing with a 4 prefix (wanting you to enter 43202 for example).  This would restrict the address range Kepware would want to request to only 10000 registers max (from data model address 1 to 9999).

By the looks of those values supposed being returned, I suspect you are reading registers in the 40000 range (and not 3200).  Current average isn't even the average of the 3 current phases.

I believe you should attempt to read PDM address 3000 (PDU address 2999) and read those 4 addresses which should be the current readings as shown below from the iEM3xxx User Guide

Robert_Lee_1-1731002176794.png

Robert_Lee_2-1731002432413.png

Also note that the current readings are returned in FLOAT32 (IEEE-754) while the kWh ones are returned using INT64 (low to high order) and by the looks of that addressing, Kepware should be requesting PDM address 3204 (or PDU address 3203) and asking for 4 registers (since it is INT64 in size).




See Answer In Context

Reply
Replies 6
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-11-05 12:26 PM . Last Modified: ‎2024-11-05 12:26 PM

0 Likes
0
1247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-05 12:26 PM

Looking at my documentation for the iEM32xx devices the kWh registers are in the 32xx range (and not in 45xxx or 5xxx depending on how KepserverEX is using that address (either implied as 4xxxx to perform a Read Holding register or simply as xxxx).  In other words, in some cases, our map might indicate to read 45xxx and that is what the Read Holding register would ask for (and not just 5xxx).  

Most =S= documentation do not imply addresses and are listed as 1 to 65535.

 

Robert_Lee_0-1730838303192.png


So it looks like you'd want to request 3203, with 2 registers to get the FLOAT32.

This assumes that to read current Ph A your doing a read of register 2999 of 2 registers as well

Reply
ChickenRich
Crewman ChickenRich
Crewman

Posted: ‎2024-11-07 02:14 AM

0 Likes
2
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 02:14 AM

Thank you for your reply Robert, I've also tried 3203; with Kepware to read a holding register, the address has to start with 4 so the 3023 becomes 43203, but with the addressing shift it becomes 43204. I've attached the client output.  I've also used Wireshark to capture the packets on both platforms to compare, but that's out of my knowledge base.  I've asked the same question on the KepServer forums too.  Hopefully someone has seen this before.  I don't think it's an issue with the Schneider meter as they work fine with Ignition.

Attachments
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-07 09:03 AM

0 Likes
1
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 09:03 AM

Hello @ChickenRich 

Did you try with Address shift the other direction, 43202?   Are you able to collect 16 register readings with modbus and from front panel of the meter to see if there could be a way to explain what the meter is returning?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2024-11-07 09:56 AM . Last Modified: ‎2024-11-07 10:12 AM

0 Likes
1
1193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-07 09:56 AM

Most present Schneider documentation states the Modbus address using standard Modbus Power Data Model (PDM) addressing.  In some instances, products may be published using PDU addressing (which is the address sent over communication to the actual device).

Now, I don't know how Kepware wants the address to be entered via its UI.  I would not think it would want to have users enter in Data Model addressing with a 4 prefix (wanting you to enter 43202 for example).  This would restrict the address range Kepware would want to request to only 10000 registers max (from data model address 1 to 9999).

By the looks of those values supposed being returned, I suspect you are reading registers in the 40000 range (and not 3200).  Current average isn't even the average of the 3 current phases.

I believe you should attempt to read PDM address 3000 (PDU address 2999) and read those 4 addresses which should be the current readings as shown below from the iEM3xxx User Guide

Robert_Lee_1-1731002176794.png

Robert_Lee_2-1731002432413.png

Also note that the current readings are returned in FLOAT32 (IEEE-754) while the kWh ones are returned using INT64 (low to high order) and by the looks of that addressing, Kepware should be requesting PDM address 3204 (or PDU address 3203) and asking for 4 registers (since it is INT64 in size).




Reply
ChickenRich
Crewman ChickenRich
Crewman

Posted: ‎2024-11-08 08:02 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-08 08:02 AM

Hi Charles, I have tried all options.  Kepserver does not like to read the registers at all, whereas Ignition reads them perfectly.  I understand that this is not a Schneider issue, and have contacted Kepware support who are assisting.  It is really strange!

Many thanks,

Reply
ChickenRich
Crewman ChickenRich
Crewman

Posted: ‎2024-11-08 08:05 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-08 08:05 AM

Thank you Robert for your reply.  This isn't a Schneider issue, it is a Kepserver issue and so I've raised a support request with them.  Just for your information, ignition reads the values perfectly, even if we're using zero based addressing which normally means the the 4 is omitted hence 43202 becomes 3202 and so on.  Many thanks for your help though.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now