Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

IEM3255 - Write to register (function code 16) issue

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • IEM3255 - Write to register (function code 16) issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
shlomiAlk
Crewman shlomiAlk
Crewman

Posted: ‎2022-06-09 12:58 AM

1 Like
3
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-09 12:58 AM

IEM3255 - Write to register (function code 16) issue

 

Hi,

 

I was trying to write CT value (address = 0x7ED, function code: 16 (10Hex)) by Modbus Poll but it doesn't work - I do success to read the registers (frequency, voltage for example without any problem).

The meter connected to my PC by RS485 to USB converter device.

 

I verified that the "Communication Protection" is disable and the multi traffic is on "By communication".

 

I used Modbus Poll after it doesn't work with my private gateway board, based linux OS, to make this problem to simple.

When I tried to configure other meter by Modbus writing command - no issue.

 

Do I need to add termination resistance?

do you have any other idea to solve it? things that I need to verify?

 

 

Thanks:)

 

modbusPollIEM.JPG

 

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2022-06-13 04:39 AM

2 Likes
2
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-13 04:39 AM

Hello @shlomiAlk 

 

The Modbus register 2004 to 2036 are the meter setup and status registers and it does not allow to write directly using function code 16.

 

You can refer the user manual page 40 and above for the Modbus command interface. 

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=DOCA0005EN-13.pdf&p... 

 

The CT parameter can not write alone, we need to follow the command number 2000 (set wiring command - page 41) using the function code 16 to change the CT primary and secondary along with few other parameters.

 

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 3
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2022-06-13 04:39 AM

2 Likes
2
1584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-13 04:39 AM

Hello @shlomiAlk 

 

The Modbus register 2004 to 2036 are the meter setup and status registers and it does not allow to write directly using function code 16.

 

You can refer the user manual page 40 and above for the Modbus command interface. 

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=DOCA0005EN-13.pdf&p... 

 

The CT parameter can not write alone, we need to follow the command number 2000 (set wiring command - page 41) using the function code 16 to change the CT primary and secondary along with few other parameters.

 

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
shlomiAlk
Crewman shlomiAlk
Crewman

Posted: ‎2022-08-01 03:26 AM . Last Modified: ‎2022-08-01 04:48 AM

0 Likes
1
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-01 03:26 AM

Hi @Ramasamy_N ,

thanks for your reply.

 

I implemented code that send one block for all "Set Wiring" registers with one value changing of "CT Primary" to be 6002 (except CT Secondary, since isn't supported in IEM3255) and I got Meter result register ok (Cmd Reg result = 5376 return 0). When I read the "CT Primary" register, it doesn't changed (I verified by reading direct from Meter display).

I sniffed the bus and parse the data - please see the attached files.

 

I verified that the communication protected is enabled.

 

Do I need to do some action before I send Modbus set command?

I'm a little stuck with this issue and I would like for any assistance here.

 

BDY, I also send one block direct from ModbusPoll software to isolate the problem (maybe I have something wrong in my code) and it doesn't work.

 

many thanks.

 

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Commander Ramasamy_N Commander
Commander

Posted: ‎2022-08-01 05:19 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-01 05:19 AM

Hello @shlomiAlk 

 

The Communication protection must be disabled during the Modbus writing. 

Also the refer the attached screenshot of Wireshark traces when we write the set wiring command. 

The 24 parameters must filled properly and you can read the CT primary from the register 2030 (UINT16 format). 

 

Regards, 

Ramasamy N

Attachments
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.