Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the Schneider Electric Community! We have moved to a new address: community.se.com — bookmark it today and contact SchneiderCommunity.Support@se.com if you have any questions!
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82794members
350631posts

IEC 61850

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
ken_newsome_gpt
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
1
409

IEC 61850

Is it possible to map, custom registers to the IEC 61850 values in a 7650 meter, so that a customer could read downstream data from a Modbus Slave device via the meters 61850 protocol?

Tags (5)

Accepted Solutions
sesa105048_brid
Lieutenant Lieutenant
Lieutenant

Re: IEC 61850

Yes, on GGIO Custom Digital and GGIO Custom Analog modules it is possible to map  16 status bits and 16 measurements as analog values.

See Answer In Context

1 Reply 1
sesa105048_brid
Lieutenant Lieutenant
Lieutenant

Re: IEC 61850

Yes, on GGIO Custom Digital and GGIO Custom Analog modules it is possible to map  16 status bits and 16 measurements as analog values.