Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
How to identify impedance of LPVT is sufficient to ION9000 voltage input impedance ?
Details:
- LPVT impedance = 10MOhm
- ION9000 impedance = 5MOhm
Link copied. Please paste this link to share this article on your social media post.
Hello @Aduldech ,
I have never used LPVT transducers before so I cannot speak to how effective they could be with ION9000 meters. Meter's voltage inputs are expecting a sinusoidal voltage input, 57 - 400 V L-N / 100 - 690 V L-L (RMS).
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Aduldech ,
ION9000 meters do not support Low Power VTs. ION ION9000 meters do support LVCTs.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Charles_Murison
In case I connect LPVT to LPVT hub. Then, converting to voltage 110V/sqrt(3) by LPVT transducer.
The LPVT transducer able to supply voltage to ION9000?
In addition, Is it sufficient that we consider burden that LPVT transducer supply to ION9000. How does the impedance affects to LPVT transducer and our meter?
Best regards,
Aduldech S.
Link copied. Please paste this link to share this article on your social media post.
Hello @Aduldech ,
I have never used LPVT transducers before so I cannot speak to how effective they could be with ION9000 meters. Meter's voltage inputs are expecting a sinusoidal voltage input, 57 - 400 V L-N / 100 - 690 V L-L (RMS).
Regards,
Charles
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.