How to identify impedance of LPVT is sufficient to ION9000 voltage input impedance ?
Metering & Power Quality
  • EcoStruxure Power & Grid
  • How to identify impedance of LPVT is sufficient to ION9000 voltage input impedance ?
Charles_Murison
Picard Charles_Murison Picard
529
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
139
Ramasamy_N
Captain Ramasamy_N Captain
115
Aduldech
Aduldech Cadet
Cadet
Posted: ‎2025-09-04 02:08 AM
568
Details:
- LPVT impedance = 10MOhm
- ION9000 impedance = 5MOhm
  • ION9000
Tags (3)
  • ion9000
  • LPVT
Charles_Murison
Posted: ‎2025-09-08 10:38 AM
Hello @Aduldech ,
I have never used LPVT transducers before so I cannot speak to how effective they could be with ION9000 meters. Meter's voltage inputs are expecting a sinusoidal voltage input, 57 - 400 V L-N / 100 - 690 V L-L (RMS).
Charles
Charles_Murison
Posted: ‎2025-09-04 08:48 AM
556
Hello @Aduldech ,
ION9000 meters do not support Low Power VTs. ION ION9000 meters do support LVCTs.
Charles
Aduldech
Aduldech Cadet
Cadet
Posted: ‎2025-09-04 08:14 PM . Last Modified: ‎2025-09-04 08:14 PM
546
Hello @Charles_Murison
In case I connect LPVT to LPVT hub. Then, converting to voltage 110V/sqrt(3) by LPVT transducer.
The LPVT transducer able to supply voltage to ION9000?
In addition, Is it sufficient that we consider burden that LPVT transducer supply to ION9000. How does the impedance affects to LPVT transducer and our meter?
Best regards,
Aduldech S.
Charles_Murison
Hello @Aduldech ,
Charles