There have 24 alarm setup in the meter front panel and 15 items can be disabled by to switch the control object from the meter default dgm on VISTA.
Can not find the control object to Enable/Disable the 4-30 Volt Intrp Ph1/2/3 at the meter default dgm but a "4-30 Enable" ext bool module has already in the meter default framework, user can Enable/Disable the "4-30 Volt Intrp" alarm by add a control object to the meter dgm and link to that ext bool module.
Still having 8 alarm setup items could not disable and no any exists ext bool module for those alarm setup.
Check the alarming configurations in the Designer and those alarm are created in either setpoint or relative setpoint modules but "Enable" input were empty.
How to disable the alarms as shown like the below pictures?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You are right that those 8 setpoint modules don't have their Enable input linked and therefore can't be disabled. We can look into adding enable links to them in the factory framework. Meanwhile, you can add a Ext Pulse module to the PM8000 framework to disable all these 8 setpoint modules but you will have to do it for each PM8000 you have. How many PM8000s do you have?
Link copied. Please paste this link to share this article on your social media post.
There are 2 job site, each job site have around 160 PM8000 installed.
Client wants to disable all the alarm setup items except the voltage sag/swell alarm and DI alarm.
Can you tell us what are the factory default label/register name for that 8 check box objects at meter alarm setup page ?
Link copied. Please paste this link to share this article on your social media post.
I looked into it again. You can actually disable those alarms in ION Setup.
1. Open your meter in ION Setup
2. Select and edit an alarm
3. Check the Force Off option and Save
4 Force Off disables the alarm
Here are the 8 alarms you need to disable but unfortunately you will have to disable each of them on each of your PM8000:
Link copied. Please paste this link to share this article on your social media post.
Is there a particular reason the customer wants to disable all these alarms?
Link copied. Please paste this link to share this article on your social media post.
I was doing the same thing as your mentioned.
Is possible to consider to implement that within next firmware release and to have the ability to edit or remove factory display pages on PM8K?
Link copied. Please paste this link to share this article on your social media post.
That was due to the front panel fault led will blinking when the alarm appears, if we can having the function to ack the alarms from remote i.e. Vista page. The fault led blinking is troubled to their operator.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Do you know that you can acknowledge alarms on the meter itself?
Link copied. Please paste this link to share this article on your social media post.
I know it can acknowledge on meter pad key and what exactly you mean on itself?
Link copied. Please paste this link to share this article on your social media post.
That was what I meant. Acknowledging alarms on meter's front panel.
Link copied. Please paste this link to share this article on your social media post.
Default alarm is very annoying to the new install site there is no voltage at line input those meters kept on alarming.
I have answered many customer who kept asking until I have change to connect them to network then it was the time to disable them all. Hope next shipment all of the factory default alarm would be off.
Link copied. Please paste this link to share this article on your social media post.
It is a good idea to fixed it at all by the default setting.
Link copied. Please paste this link to share this article on your social media post.
Lately I did disable all alarm of the ION7400 then save the framework for other ION7400 to be installed.
Link copied. Please paste this link to share this article on your social media post.
Latest update I switched the EB28 to off to stop 4-30 10 minutes evaluate because it sent event to event log every 10 minutes when complete installation with line energized every thing will be review again whether to re-activate all off items or not.