Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

How to Configure ion7550 communication by ICE61850

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to Configure ion7550 communication by ICE61850
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Anonymous user
Not applicable

Posted: ‎2017-03-27 07:14 PM

0 Likes
2
1181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-27 07:14 PM

How to Configure ion7550 communication by ICE61850

Hi all,

I'm configuring ion7550 communication by iec61850 using ion setup.

-> Missing CID file

So how to configure ION communication using iec61850.

Thanks.

Ta Cong

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
sesa64419
sesa64419 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2017-03-28 08:09 AM

3 Likes
0
1117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-03-28 08:09 AM

Hello

To get IEC 61850 working on your meter, it is a process.

1. Get the ICD file that matches the hardware of your device from Schneider Electric. The ION7550 v360 ICD files are located here: **they are also available inside the CET850 program**

http://www.schneider-electric.com/en/download/document/ION7550_v360_ICD_files/

2. Next, you must convert the ICD file to a CID file using a configuration tool such as CET850:

http://www.schneider-electric.com/en/download/document/CET850+IEC850+configuration+tool/

3. Run CET850. Chose File > New. Go to Add > IED. Navigate to where you have stored your ICD file (or select device from library). Enter in the name, description and Ethernet information for your device, then click OK. Go to File > Build all CID files. Select a location, enter a file name and click Save. Do not change the file type (leave as SCD).

4. Load your CID file onto your ION7550. You can do this via FTP, but using ION Setup will show you if the file has loaded correctly. You may need to update your version of ION Setup to get the Load functionality. The latest ION Setup is located here, or by going to your existing ION Setup program and selecting Help > check for update:

https://schneider-electric.app.box.com/ionsetuplatest

5. In ION Setup, navigate to your device and select the IEC 61850 tab. Click Upload, and navigate to where you have stored your CID file. The CID status will indicate that the CID file is being parsed, and then will indicate "IEC 61850 stack running" if the CID file is valid and loaded correctly. At that time you will have IEC 61850 functioning on your meter.

IEC68150_running.png

This is described in the IEC 61850 and ION meters protocol document, which gives more detail about how IEC 61850 is implemented in your meter, available from Schneider Electric here:

http://www.schneider-electric.com/en/download/document/70022-0125/

And also described in the Third Party Protocols chapter of the ION7550/ION7650 user guide, available here:

http://www.powerlogic.com/literature/7550-7650_User_Guide_70002-0248-07.pdf

You can also refer to the PM8000 user guide, communications chapter, as the implementation/feature is the same as the ION7550:http://www.schneider-electric.us/en/download/document/7EN02-0336/

Regards,

Alana

Reply
Anonymous user
Not applicable

Posted: ‎2017-04-14 10:48 PM

0 Likes
0
1117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-04-14 10:48 PM

Hi Alana,

Thanks, I have successfully loaded the CID file into ION.

Ta Cong

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now