Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to connect an ION module's input to a setup register using ION Setup

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How to connect an ION module's input to a setup register using ION Setup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Start a Topic
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2013-02-28 06:49 PM . Last Modified: ‎2020-04-22 01:56 AM

0 Likes
2
2215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-02-28 06:49 PM

How to connect an ION module's input to a setup register using ION Setup

Certain ION modules will allow inputs to be connect to another module's setup register (ex. Nominal Voltage in the Sag/Swell module).  Most common application would be pulling a numeric setup register into one of the inputs of an Arithmetic module.

 

The procedure is as follows:

 

  1. Exit any table/dialog and at the network view, display the device properties (either via the Edit menu or right clicking on the device icon).
  2. Click on the Tools tab and switch the Device Setup to "Show Advanced ION Setup" then click on OK.  This should show all the ION module types if viewing the device setup type.
  3. Find the module type which contains the setup register and bring up all the modules, selecting the one you want to connect the input to.
  4. When the module dialog appears, hold down the <Ctrl> key and then click on the Setup register tab shown in the dialog.  This will show all the setup register but instead of showing the setup register value next to the labels, it will show the register address (shown in hexadecimal ex. 0x721A for the SS1 Nom Volts setup register).  Make note of the register address for later reference.
  5. Exit the dialog and find the module type which you wish to connect the input from and bring up the module you wish to connect from.  Hold down the <Ctrl> key and then click on the Edit button on the Input dialog to bring up the Input selection dialog.
  6. In the Parameter edit box, enter the hexadecimal address of the setup register you noted in step 4.  Press the Search button and the edit box should fill in with the name of the setup register if done properly.  Click OK to set the input to the setup register, then press Send to send the changes to the device.
  7. Switch the Device Setup back to "Show Basic ION Setup" doing the reverse of steps 1 and 2.

 

Restrictions:

 

Only numeric variable setup registers can be linked (i.e. enumerated setup registers like PM1 Volts Mode won't work)

Pulse/Boolean type inputs can't be connected

Labels
  • Labels:
  • ION Setup
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Yu_Diao
Yu_Diao Leader
Leader

Posted: ‎2013-03-05 05:24 PM

0 Likes
1
2159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-03-05 05:24 PM

Robert,

Not sure if this is your expertise or not, but wonder if you know how I can do the same thing in designer?

I know you can directly link the input to a ION register address by Ctrl+Alt+click the "ION" icon in the toolbar which corresponds to setup 5 in your post, but where to find the desired ION handle register address?

Regards,

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2013-03-05 05:50 PM

0 Likes
0
2159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-03-05 05:50 PM

It's been a few years since I've tried this but I believe if you hold just Ctrl (or maybe its Alt or maybe Shift?) when you click on the ION icon on the toolbar in Designer, the dialog will list Setup registers instead of Output registers as you click on the modules.

Reply

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore