I'd like to know about the max number of ION9000's records.
I think that the max number of the records are below.
・Events:5000
・Historical Alarms:25
・Active Alarms:??
Do you have any idea?
Regards,
Okada
Link copied. Please paste this link to share this article on your social media post.
The Event Log Controller default depth is 5000, but can be user configured to a maximum of 20000. These events can be viewed on the display and/or read over comms with ION protocol.
"Alarms" are not accessible over comms nor web and only viewable on the display interface.
Active Alarms: every possible alarm source has a reserved position. In total, there are up to 148 alarm sources visible on the display only.
Historical Alarms: depth of 25 visible on the display only
Dan
Link copied. Please paste this link to share this article on your social media post.
The Event Log Controller default depth is 5000, but can be user configured to a maximum of 20000. These events can be viewed on the display and/or read over comms with ION protocol.
"Alarms" are not accessible over comms nor web and only viewable on the display interface.
Active Alarms: every possible alarm source has a reserved position. In total, there are up to 148 alarm sources visible on the display only.
Historical Alarms: depth of 25 visible on the display only
Dan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
The PM8000 has basically the same capabilities in these regards.