Hi all:
I need to get the last sag and swell Voltage value.
And i'm using PME designer for store the value and output it to modbus.
For now I use the diststart as time for store module to store the value of sag.
But the time is not really the sag start time. Can't get the really sag voltage value.
How can I correctly get the last sag voltage volue for V1~3?
Any hint will help. Thanks
Link copied. Please paste this link to share this article on your social media post.
The disturbance magnitude and duration outputs of the SAG/SWELL module are updated at the 'DistEnd' event.
Much like DRE5 (Sag/Swell Log), you'd want to link the 'Store' input to the 'DistEnd' trigger output.
Link copied. Please paste this link to share this article on your social media post.
The disturbance magnitude and duration outputs of the SAG/SWELL module are updated at the 'DistEnd' event.
Much like DRE5 (Sag/Swell Log), you'd want to link the 'Store' input to the 'DistEnd' trigger output.
Posted: 2022-05-25 08:16 PM . Last Modified: 2022-05-25 08:53 PM
Link copied. Please paste this link to share this article on your social media post.
Hi @DanL
Thanks for reply.
If I use this for store time.
Can it compare with the % that PME's alarm shows? or 9000's on board alarm?
Cause I'm not able to fully create a sag event at my office.
So I'm not sure if the real sag event will make all of this same or close enough.
Thanks