Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How can I configure the IEEE 519 module in the ion 7400 meter?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • How can I configure the IEEE 519 module in the ion 7400 meter?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
570
Mehran_Mehrnia
Mehran_Mehrnia Champion
202
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
PowerLogic
PowerLogic ION7400 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-27 07:14 AM

0 Likes
7
3576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-27 07:14 AM

How can I configure the IEEE 519 module in the ion 7400 meter?

 

Very good to everyone.
I have a problem with the configuration of the @ION7400 @ION7000 to generate the power quality reports, it sends me an error that is shown in the  following image,

Hint:

 

In the VISTA it sends me another error about this standard @Power Quality,

 
 
 
 
 
Hint:

 

@ links to members, content

image.png@Power Quality

Image of a previous @ION Setup version mentioned in the manual, where the IEEE 519 module could be configured

image.png

Image of ION Setup @ION Setup 3.1.19, you do not have to configure IEEE 519 of @Power Quality

image.png

 

According to the ION @ION Setup manual it has the way to configure but in versions 3.1 and actucal 3.2 it does not have this option, in any case maybe in version 3.016 someone can provide it to me or how could I configure the framework ieee 519 in ION 7400 @ION7000, thank you very much for your attention.

 

@Power Quality

@ION Setup

  • Thumbnail of PowerLogic ION7400 series
    PowerLogic
    PowerLogic ION7400 series
View products (1)
Labels
  • Labels:
  • ION Setup
  • ION7000
  • Power Quality
Tags (2)
  • Tags:
  • english
  • Englsh
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-08-02 04:34 PM

3 Likes
1
3514
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-02 04:34 PM

Hello @Anonymous user ,

 

In ION Setup, with the setup assistant close, if you right click on the meter in the left hand panel, and select properties, there should be a pop-up. One tab on this popup should be display, what is the option you have for your meter? If you change the display, does the Setup assistant give you the option you desire? If not I strongly recommend contacting technical support (se.com->support->contact support) to begin a case to troubleshoot. Tech support my ask for a packet capture between ION Setup and the meter from before ION Setup connects to the meter until after you select the Advanced PQ tab. Wireshark is an example of how you can capture that information.

 

7400_display.jpg 

 

Regards,
Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2021-07-27 11:31 AM

0 Likes
1
3562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-27 11:31 AM

Hi John

 

What is the firmware version and the framework version?

 

Thanks


Tom

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-07-27 12:00 PM

0 Likes
4
3560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-07-27 12:00 PM

Hello @Anonymous user ,

 

The screen shot below is for ION9000T but the steps would be the same
Power Quality -> Advanced PQ -> 519 -> EditIEEE519.jpg

Clicking the edit button should bring up a window for IEEE 519 Configuration where you can set the voltage, short circuit current, demand current.

There could be a few different reasons why your version of ION Setup does not look the exact same as mine. Version of ION Setup is a start. Anything below V3.2 is old. V3.2 itself has a number of versions. The build number can give you a hint when your version is from, V3.2.21XXX is released this year. If your version of ION Setup is recient, the next place to look is firmware version as Tom said. Old versions of firmware such as V1.4.3 may not have had the capacity to include multiple PQ standards on the meter at the same time. Later versions of firmware and templates included the modules required to support IEEE519. The modules do need to be configured and activated before meter will calculate required information for the PME reports.

 

Regards

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-08-02 07:19 AM

0 Likes
0
3529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-02 07:19 AM

Hi @Tom_Stevenson

 

The ION7400 version is:

 

image.png

 

Thanks for your support.

 

John

 

 

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-08-02 07:31 AM

0 Likes
3
3526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-02 07:31 AM

Hi @Charles_Murison.

 

Well, the version that I have of the ION setup is the last one, previously it was with the IONSetup version v3.1.19095.01, it did not appear there either because I decided to install the latest version which is: IONSetup v3.2.21188.01, in the same way it does not appear to me now in the version of the ION7400 it is the one shown in the image:

image.png

 

To do the configuration of the standard ieee 519 I do not see more than the following options.

 

image.png

In any case, if it is a firmware issue for the ION7400, it is recommended to update it?

Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-08-02 07:40 AM

0 Likes
2
3523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-02 07:40 AM

Hi @Charles_Murison 

As indicated, look for a way to enable this standard but the truth is that the ION setup did not show me the steps of the guide system.

However the framework does appear.

 
 

image.png

 

Thank you very much for your support

 

 

John

 

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-08-02 04:34 PM

3 Likes
1
3515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-02 04:34 PM

Hello @Anonymous user ,

 

In ION Setup, with the setup assistant close, if you right click on the meter in the left hand panel, and select properties, there should be a pop-up. One tab on this popup should be display, what is the option you have for your meter? If you change the display, does the Setup assistant give you the option you desire? If not I strongly recommend contacting technical support (se.com->support->contact support) to begin a case to troubleshoot. Tech support my ask for a packet capture between ION Setup and the meter from before ION Setup connects to the meter until after you select the Advanced PQ tab. Wireshark is an example of how you can capture that information.

 

7400_display.jpg 

 

Regards,
Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Anonymous user
Not applicable

Posted: ‎2021-08-04 08:47 AM

0 Likes
0
3502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-08-04 08:47 AM

hi @Charles_Murison 

 

Thank you very much for the support, it already worked.

 

Regards.

 

 

John

 

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore