Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Have you ever wondered how many logs your ION meter can store?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Have you ever wondered how many logs your ION meter can store?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Sanjeet_Sahota
Sanjeet_Sahota Mentor
Mentor

Posted: ‎2020-01-06 04:10 PM

5 Likes
1
2964
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-06 04:10 PM

Have you ever wondered how many logs your ION meter can store?

With the need to record more data than ever, it can be a challenge to balance the number of logs stored on a device against a fixed memory space and how frequently data is being recorded.   However, with the use of ION technology we have been able to minimize the memory footprint each data log requires to allow for more data to be stored.

With ION meters allowing up to 50 data recorder modules, with 16 inputs each, calculating the amount of space required for logs becomes a necessity to maximize the information needed.  This can also be used to understand how much data is being consumed when communicating over cell modem. This will provide a rough estimate on the amount data that would be required when accessing the meter allowing you to pick the right data plan for your device.

 

 Below outlines how much memory is required to store a single log of data:

Datarecorder Formula.png

 

Using this formula, the amount of memory used by a single data recorder can be calculated under certain conditions. See below for example:

# Channels

Log interval (mins)

Days of Data storage

Depth

kB Used

16

15

120

11520

990

 

Datarecorder Formula FIlled in.png

 

Similarly, Waveform Recorders use the same memory pool as the Data Recorders. You can also calculate the amount of memory required for your Waveform Recorders:

 

Waveform Formula.png

 

 

*Sample Rate & Cycles Per Capture* - This is as configured in the Waveform Recorder as seen in the screenshot below:

 

IONseutp.png

 

Filling in the formula above using the setup from the screenshot above, you can calculate the total capacity to be:

Depth Setting

Sample Rate

Cycles per Capture

kB Used

30

1024

2

122

 

Attached to this post is a basic Excel template that can be used to determine how much memory your current configuration is using.  All cells highlighted in grey can be modified to help calculate your memory usage.  Make the most of your data!

 

Attachments
Memory_and_logging_calculation_tool_spreadsheet_for_ION.xls
Tags (5)
  • Tags:
  • data recorders
  • depth
  • logging
  • memory
  • revenue log
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-02-26 09:12 AM

1 Like
0
2932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 09:12 AM

Hello @Sanjeet_Sahota,

 

Thank you for sharing this useful information with the community. 🙂

 

See Answer In Context

Reply
Reply 1
Anonymous user
Not applicable

Posted: ‎2020-02-26 09:12 AM

1 Like
0
2932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-26 09:12 AM

Hello @Sanjeet_Sahota,

 

Thank you for sharing this useful information with the community. 🙂

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore