Hi,
Can anyone offer any assistance with the following issues that we are constantly seeing with installation and testing of HDPM6000 systems?
Normally we are using the 42 channel HDPM6000R interface in IEC channel configuration mode. After the basic commissioning, setting up CT types and channels, etc, we are seeing the following issues:
If anyone can suggest methods of getting the information to display in a real time manner, this would be a great benefit.
Regards,
Brian
Link copied. Please paste this link to share this article on your social media post.
Hi @BrianW
You did not mention the firmware version of the HMI whether it is V1.0(the old version) or V2.0, which has some improvements.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @BrianW
You did not mention the firmware version of the HMI whether it is V1.0(the old version) or V2.0, which has some improvements.