Frequency N1 or N2 Count Event
I looked in my PME Event log and I am seeing a TON of Frequency N1 Count and Frequency N2 Count events where the condition is Incremented and the Value is Limit Exceeded. Every 10 seconds.
I am not sure how to correct this issue. It is an ION 7650 and the FAC1 NomFreq is set to 60Hz however this meter is on a 50Hz system. I have other meters in similar conditions but this is the only one filling up the event log. The meter won't let me change the NomFreq.
Link copied. Please paste this link to share this article on your social media post.
2017-12-2412:14 PM
Short answer, the Nominal Frequency is set at the factory as determined by the model number when purchased. This register is used in a number of places so it is important to purchase the correct Frequency version for the application.
Link copied. Please paste this link to share this article on your social media post.
2017-12-2412:14 PM
Short answer, the Nominal Frequency is set at the factory as determined by the model number when purchased. This register is used in a number of places so it is important to purchase the correct Frequency version for the application.