Hi, We have a number of PM5561 with a current firmware version of V10.1.0.0. We have tried to upgrade to V12.0.4 (which is the lowest firmware version we have been able to find) using the upgrade tool, but it fails.
Maintenance - Firmware Upgrade (Snippet from User Guide).pdf only shows how to upgrade from 10.6.X
Does anyone know how to get from 10.1.0.0 to 10.6.X and where can I find 10.6.X and 10.9.9 firmware?
Please let me know if you need further information to assist.
Thanks in advance
Tom
Link copied. Please paste this link to share this article on your social media post.
Hi @tak20 ,
The PM5561 can only be upgraded when the firmware is version 10.6.4 or higher. Earlier firmware versions cannot be upgraded.
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
Hi @tak20 ,
The PM5561 can only be upgraded when the firmware is version 10.6.4 or higher. Earlier firmware versions cannot be upgraded.
Regards,
JD
Link copied. Please paste this link to share this article on your social media post.
So what are we supposed to do with all our PM5560s which are not secure? Do we just have to throw them away?
Link copied. Please paste this link to share this article on your social media post.
Hi @tak20,
I would suggest contacting your country's local support office. They will provide the best options for you.
Link copied. Please paste this link to share this article on your social media post.
Thanks