FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Anonymous user
Not applicable

Posted: ‎2015-07-03 05:05 AM . Last Modified: ‎2020-04-20 05:37 AM

0 Likes
1
642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-03 05:05 AM

FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?

With IM10/20 range and IM400 range an hysteresis principle is apply with threshold alarm and prealarm levels

 

the principle is :

alarm is activated when default is at the threshold value; alarm is desactivated when default is 20% higher than threshold value. This is to avoid on/off alarm switching when a default is closed to the threshold

 

The same principle exists with old range XM/XML

Labels
  • Labels:
  • Insulation Monitoring
Tags (1)
  • Tags:
  • hysteresis
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Madleen_Laclef
Lt. Commander Madleen_Laclef Lt. Commander
Lt. Commander

Posted: ‎2015-07-16 08:20 AM

0 Likes
0
623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-07-16 08:20 AM

An application note was just written explaining this hysteresis principle.

The purpose of this characteristic of the product is to ensure that if the insulation level fluctuates around the alarm threshold, the customer does not get many flickering alarms.

Notice that the competition IMDs (Bender...) use the same principle.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of