FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2015-07-0305:05 AM
FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?
With IM10/20 range and IM400 range an hysteresis principle is apply with threshold alarm and prealarm levels
the principle is :
alarm is activated when default is at the threshold value; alarm is desactivated when default is 20% higher than threshold value. This is to avoid on/off alarm switching when a default is closed to the threshold
Link copied. Please paste this link to share this article on your social media post.
2015-07-1608:20 AM
An application note was just written explaining this hysteresis principle.
The purpose of this characteristic of the product is to ensure that if the insulation level fluctuates around the alarm threshold, the customer does not get many flickering alarms.
Notice that the competition IMDs (Bender...) use the same principle.