FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

ChenLiang
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
197

FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?

With IM10/20 range and IM400 range an hysteresis principle is apply with threshold alarm and prealarm levels

 

the principle is :

alarm is activated when default is at the threshold value; alarm is desactivated when default is 20% higher than threshold value. This is to avoid on/off alarm switching when a default is closed to the threshold

 

The same principle exists with old range XM/XML

Tags (1)
1 Reply 1
Madleen_Laclef
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
178

Re: FAQ The alarm threshold of IM400 is set to 1Kohm, why the alarm dropout at more than 1.2-1.3Kohm?

An application note was just written explaining this hysteresis principle.

The purpose of this characteristic of the product is to ensure that if the insulation level fluctuates around the alarm threshold, the customer does not get many flickering alarms.

Notice that the competition IMDs (Bender...) use the same principle.