Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Error Setup analog output of Power Meter PM2230

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Error Setup analog output of Power Meter PM2230
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EasyLogic PM2000 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Kanon.w
Kanon.w
Explorer

Posted: ‎2025-09-25 11:06 PM

0 Likes
3
2619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-25 11:06 PM

Error Setup analog output of Power Meter PM2230

Trying to setup analog output of Active Power for PM2230 in IONsetup. It is giving me error when I send to power meter the parameter.

 

Following this FAQ Setup analog output of Power Meter PM2230 | Schneider Electric Thailand

I assume the 4mA = 10 kW and 20mA = 100kW

 

So I want to setup mine as 4mA = 0 kW and 20mA = 600kW

however, it gives me error upon sending to PM2230.

 

Thank you in advance for your assistance.

  • Thumbnail of EasyLogic PM2000 series
    Schneider Electric
    EasyLogic PM2000 series
View products (1)
Attachments
Labels
  • Labels:
  • ION Setup
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Sidharthan
Sidharthan Contributor
Contributor

Posted: ‎2025-09-29 10:46 PM . Last Modified: ‎2025-09-29 10:47 PM

1 Like
1
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-29 10:46 PM

@Kanon.w  I tried to reproduce the issue, 

Observations:

  1. Once we set the analog output as above and click send, we are getting Invalid Parameter#1 and 2 message in ION setup, but the settings are successfully sent to meter, and analog output is working as the settings.
  2. When we set the Analog Input 1 and 2 to some values and then edit analog output 1 and then clicking send button, the error message is not appearing.
  3. Need to further check with ION Setup team, why it is necessary to setup both analog input and output at the same time.

See Answer In Context

Reply
Replies 3
Sidharthan
Sidharthan Contributor
Contributor

Posted: ‎2025-09-29 10:46 PM . Last Modified: ‎2025-09-29 10:47 PM

1 Like
1
2563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-29 10:46 PM

@Kanon.w  I tried to reproduce the issue, 

Observations:

  1. Once we set the analog output as above and click send, we are getting Invalid Parameter#1 and 2 message in ION setup, but the settings are successfully sent to meter, and analog output is working as the settings.
  2. When we set the Analog Input 1 and 2 to some values and then edit analog output 1 and then clicking send button, the error message is not appearing.
  3. Need to further check with ION Setup team, why it is necessary to setup both analog input and output at the same time.
Reply
Kanon.w
Kanon.w
Explorer

Posted: ‎2025-10-02 05:38 PM

0 Likes
0
2483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-02 05:38 PM

Thanks for the reply Sidharthan, I tried putting in the AI and the error won't pop up anymore but I don't know if it works or not. Is there a way to contact ION Setup team? 

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-10-03 10:01 AM

0 Likes
0
2470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-03 10:01 AM

Hi @Robert_Lee 

 

Could you please share your thoughts on this behavior?

 

Thank you.

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore