If several meters of reference A9MEM3350 are throwing errors 203/204 which are being used in photovoltaic systems. It is understandable, that this problem is caused by a wiring issue and phase sequence issue. *(Assume no config, phase and wiring issue)
Lets say these meters are not 4 quadrant meters, so they would not be measuring imported-exported energy. Is it a suitable choice then in a sense that it would work in this kind of setup (photovoltaic generation) at all or no and might be causing these errors?
Will these two errors (203/204) could be caused by the fact that sometimes the current might be circulating backwards on the CT, due to the photovoltaic production and causing these errors?
I will really appreciate any comments in this matter to clear up these doubts.
Thank You!
Yours,
AK
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
203 - phase sequence reversed is only a voltage thing, the phase angle of current does not apply.
204 - Yes if current is flowing from load to line, yes you would see this error code.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @Asif_Khan ,
203 - phase sequence reversed is only a voltage thing, the phase angle of current does not apply.
204 - Yes if current is flowing from load to line, yes you would see this error code.
Regards,
Charles