EM35xx and Rogowski Rope CT's

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • EM35xx and Rogowski Rope CT's
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa277738_brid
Ensign sesa277738_brid Ensign
Ensign

Posted: ‎2015-06-04 06:11 PM

0 Likes
4
1584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-04 06:11 PM

EM35xx and Rogowski Rope CT's

The EM3550 and it's EM35xx family can directly accept Rogowski ct's, but how does this effect the CT ratio programmed in the meter?


This version of Rogowski CT I am dealing with can accept values from 20-5000 Amps but I am not exactly sure how this scales to our meter.


The default programmed CT ratio in an EM35xx is 100:5, does this need to be modified for proper operation?







Tags (4)
  • Tags:
  • ct
  • em3500
  • em3550
  • rogowski
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Mark_Raftery
Ensign Mark_Raftery Ensign
Ensign

Posted: ‎2015-06-05 01:11 AM

0 Likes
3
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-05 01:11 AM

Hi Brendan,

I was not aware that you could use Rogowski CT's with this range. The output from this coil I a voltage proportional to the current, so there would need to be a selection in the meter between current (Normal CT's) and voltage to enable the scaling on voltage to current.

The only thing that I have been looking at is a converter for Rogowski outputs into a current that our meters can accept.

Here is a link to the Phonix Contact coils and converters. But I have not had a project yet that I can try these out on.

https://www.phoenixcontact.com/online/portal/gb?1dmy&urile=wcm%3apath%3a/gben/web/main/products/subc...

Reply
sesa277738_brid
Ensign sesa277738_brid Ensign
Ensign

Posted: ‎2015-06-08 01:42 PM

1 Like
2
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-06-08 01:42 PM

Here is the knowledge base article on the EM35xx meters and the Rogowski CT's http://www.powerlogic.com/kbarticle.cfm?myrequest=FA233732.en_US


I think these particular meters can only accept rogowski ct's, as there is not an internal setup feature that I have found to switch between the two types of CT.

When programming the EM3500's, there are 2 CT parameters to set up:

CT V - CT Input Voltage: 1.0V or 0.33V.

CT SZ - CT Size: in Amps. Maximum is 32000 Amps.

Reply
Anonymous user
Not applicable

Posted: ‎2016-02-04 02:58 PM

0 Likes
1
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-04 02:58 PM

Hi Brendan,

Only the EM35xxA (Part number must end with "A" aka "A" version) works with the U018 Rogowski Rope CTs. The regular EM35xx meters will not accept the U018 Rogowski Rope CTs.

When programming the EM35xxA, the meter will not ask for the CT output voltage as the U018 Rope CTs are the only type it will accept. Since CT range covers 20A to 5000A, you will only program the CT size corresponding to the service. It is recommended to use the Rope CTs for 400A and above applications.

Reply
ken_newsome_gpt
Lieutenant | EcoXpert Master ken_newsome_gpt Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2018-05-31 05:36 AM

0 Likes
0
1495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-31 05:36 AM

Why wouldn't you set the CT scale to 5000A since that corresponds to the .33V output on the secondary side. Does the meter internally correct for this?

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of