Good day Team
Could you please provide clarification regarding the EM3570 meter:
Tariff switching is triggered by a change in the input status of S-In.
Will this input change cause the meter to switch registers for kWh readings, or will it continue recording on the same register?
thank you
Gladwin
Link copied. Please paste this link to share this article on your social media post.
Hi @Gladwin
In the EM3570 meter, when the S-In input triggers a tariff change, the meter switches to a different kWh register corresponding to the active tariff, allowing energy to be recorded separately for each tariff.
Best Regards,
-Mehran
L3 Expert Advanced metering
Link copied. Please paste this link to share this article on your social media post.
Hi @Gladwin
In the EM3570 meter, when the S-In input triggers a tariff change, the meter switches to a different kWh register corresponding to the active tariff, allowing energy to be recorded separately for each tariff.
Best Regards,
-Mehran
L3 Expert Advanced metering