EM1250 Datasheet question.

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
skkim_isama_net
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
1
176

EM1250 Datasheet question.

Hello H/W Team.

I’m now proposal EM1250 at customer.

I have some question.

This question all of the from customer.

A. EM1250 Rollover Value range

B. EM1250 if rollover data value raised, how to find knew old data.

I was check modbus map sheet state Previous integrator register,  what is it?

C. EM1250 current input withstand (EM1250 datasheet not display detail information, base 60Hz for time)

Tags (4)

Accepted Solutions
Mitun_Paul
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
149

Re: EM1250 Datasheet question.

A. EM1250 Rollover Value range

>> Please refer below table.
6018

B. EM1250 if rollover data value raised, how to find knew old data.

>> The new old data can be found in history page. Previous register is for historical value.

6019  6030

C. EM1250 current input withstand (EM1250 datasheet not display detail information, base 60Hz for time)

>> Please refer the below screen capture from the technical datasheet

6032

See Answer In Context

1 Reply 1
Mitun_Paul
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
150

Re: EM1250 Datasheet question.

A. EM1250 Rollover Value range

>> Please refer below table.
6018

B. EM1250 if rollover data value raised, how to find knew old data.

>> The new old data can be found in history page. Previous register is for historical value.

6019  6030

C. EM1250 current input withstand (EM1250 datasheet not display detail information, base 60Hz for time)

>> Please refer the below screen capture from the technical datasheet

6032