- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi, my customer is needing to enable his Schneider PM5560 and PM5320 meters for comms with Rockwell ethernet protocol. For this they need the EDS files.
I have managed to find the EDS for the PM5560 in the latest firmware zip. However it appears to be missing from the latest PM5320 fimware zip.
Could someone direct me to the file please?
Many thanks
Shaun
- Labels:
-
PM5000
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Shaun,
PM5300 supports only the Modbus TCP and BACnet IP protocols. It does not supports Ethernet/IP protocol.
We don't have the EDS file for PM5320.
Regards,
Ramasamy N
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Shaun,
PM5300 supports only the Modbus TCP and BACnet IP protocols. It does not supports Ethernet/IP protocol.
We don't have the EDS file for PM5320.
Regards,
Ramasamy N
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thank you for the clarification Ramasamy. I had not spotted the distinction previously.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Ramasamy,
Do you know how the PM5560 generic module Assembly input on the Rocwell Logix tags should be set up? is it DINT, INT or SINT, or anything else?. I use a generic module, and I can see the data is exchanged. (Implicit exchanges). But, it's not same as per actual data shown at the PM5560 parameter. i.e current.
Any help will be appreciated. Thank you
Best regards
Aep
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Aep,
The generic module Assembly input to be set as REAL.
Please refer the attached screenshot of configuration for more details.
Regards,
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Ramasamy,
Just changed the comm format to REAL, and then, bam! it's working. it showed the correct number. 🙂
so, thank you so much for your help!!
Best regards
Rahman

