Difference in harmonics between phases

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Difference in harmonics between phases
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
489
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
90
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
jerry_IPACS
Lieutenant JG jerry_IPACS
Lieutenant JG

Posted: ‎2020-07-08 10:04 PM . Last Modified: ‎2020-07-08 10:05 PM

0 Likes
1
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-08 10:04 PM

Difference in harmonics between phases

Hi everyone, 

 

I have been getting a strange issue from some of the ION 9000 meters that we have installed on a site recently. Some of the meters seem to have different THD measurements on phase A compared to phases B and C. For example, the THD mean measurement on phases B and C are rougly 10-15% whereas the same measurement on phase A is around 1% (refer to attached images). Its strange because the THD high measurement on all three phases is somewhat consistent, but just the THD mean measurement on phase A is off). Has anyone come across this? I was thinking that it is due to some meter firmware issue, but I have the latest versions of the firmware installed on all the meters. Any guidance would be much appreciated. 

 

Regards, 

Jerry Benny - IPACS Group
Attachments
Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2020-07-09 12:40 AM

1 Like
0
1451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 12:40 AM

Double check your software (report?) configuration.

The first attachment "Phase A.png" appears to plot the HIGH (red) current THD and MEAN (green) current THD on phase A. These do not appear to be voltage THD plots.

The second attachment "Phase B.png" does not have a legend, but presumably it is HIGH (red) current THD and MEAN (green) current THD on phase B.

There does not appear to be any phase C data nor voltage THD data.

Without knowing anything about the system being monitored, the provided plots do not look exceedingly strange to me.

 

Double check your meter is configured to log THD the way you want. THD can be configured to be %fundamental, % RMS, % Nominal, and/or % Demand.

When using %fundmantal and/or %RMS modes, high THD ratios are common when the load is very low. You may need to correlate the data with load levels to interpret the THD (or use an alternate THD mode to mitigate this effect)

 

Lastly, you should perform a "manual waveform capture" trigger and view the waveform capture

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Reply 1
DanL
Captain DanL Captain
Captain

Posted: ‎2020-07-09 12:40 AM

1 Like
0
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-07-09 12:40 AM

Double check your software (report?) configuration.

The first attachment "Phase A.png" appears to plot the HIGH (red) current THD and MEAN (green) current THD on phase A. These do not appear to be voltage THD plots.

The second attachment "Phase B.png" does not have a legend, but presumably it is HIGH (red) current THD and MEAN (green) current THD on phase B.

There does not appear to be any phase C data nor voltage THD data.

Without knowing anything about the system being monitored, the provided plots do not look exceedingly strange to me.

 

Double check your meter is configured to log THD the way you want. THD can be configured to be %fundamental, % RMS, % Nominal, and/or % Demand.

When using %fundmantal and/or %RMS modes, high THD ratios are common when the load is very low. You may need to correlate the data with load levels to interpret the THD (or use an alternate THD mode to mitigate this effect)

 

Lastly, you should perform a "manual waveform capture" trigger and view the waveform capture

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of