Hi All,
We have a site that using 7.2.3 with Sql Server 2012.
I've noticed that when I query the ION_Data.dbo.DataLog2 table, the data is 9-10 hours behind for all the meters.
Is there a setup, either within the meters (namely PM3255's), PME Management Console, or ION Setup, where we can define when the data is sent to be logged in the database?
I can query each meter in ION Setup and get real time data. Just can't cross-reference that back to database when it is 9-10 hours behind.
Cheers.
Link copied. Please paste this link to share this article on your social media post.
I believe this is happening because PME always saves all timestamp information in UTC. Is the customer system/server which you are accessing 9-10 behind UTC/GMT?
PME will always time sync a PM3255 device to server local time (PME will time sync a PM5000 series meter to UTC; so it varies from meter to meter depending on meter design). After reading the logs the timestamp will be converted to UTC and then stored in the database.
Link copied. Please paste this link to share this article on your social media post.
Hi Russell
I am tying in Anirban DHAR. It sounds similar to a firmware/driver issue that was addressed some time ago for the 3255, but I suspect that 7.2.3 (very few of these systems out there) does not have that update. Anirban DHAR, can you please confirm?
I am quite sure a move to v8.x will resolve this Russell, but Anirban will be able to confirm first.
Tom
Link copied. Please paste this link to share this article on your social media post.
I believe this is happening because PME always saves all timestamp information in UTC. Is the customer system/server which you are accessing 9-10 behind UTC/GMT?
PME will always time sync a PM3255 device to server local time (PME will time sync a PM5000 series meter to UTC; so it varies from meter to meter depending on meter design). After reading the logs the timestamp will be converted to UTC and then stored in the database.
Link copied. Please paste this link to share this article on your social media post.
Thank Anirban and Tom,
It was the UTC conversion which threw me out. We are 10.5 hours in from of UTC, so everything is lining up now.
Cheers,
Russ.