Hi All,
I am using the PM8000 to capture data (Frequency and kW) pre and post a frequency event. To do this I am using a setpoint module with a limit (for instance 49.97) that triggers a data recorder to record 5s pre event and 10s post event.
When the record is complete a LogExport module sends the data (an xml) to an email server.
As per the attached I am getting issues whereby the data/indexing in the data recorder is somehow not chronological.
Referring to the attached if you scroll to the bottom of the file the first entry is DR pos =32 and the seconds of the timestamp is 12. Scrolling up through records you will notice that at DRpos =36 the time has suddenly jumped out of chronological order.
It turns out the records DR pos 32-35 should come after DR pos 47 to make this data set chronological.
I am wondering how I could have potentially got the data recorder indexing in this state and or how to get it back to chronological order?
The settings in the Data Recorder are:
Depth = 16
RecordMode = Circular
Insert Outage Records = No
Checksum = Disabled
Buffer Depth = 128
Timestamp Mode = Record Pulse
Pre Trigger Records = 5
Post Trigger Records = 10
Within the LogExport Module the only setting I believ of note is:
Max Send Records = 16
Link copied. Please paste this link to share this article on your social media post.
Hello @ausfrosty1,
There is no setting in the meter that can force the meter to save data in a specific order. When using pre-trigger and post-trigger logging, you can't rely on the timestamps monotonically increasing with the record ID anymore. You have to use the timestamps to order the data.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @ausfrosty1,
There is no setting in the meter that can force the meter to save data in a specific order. When using pre-trigger and post-trigger logging, you can't rely on the timestamps monotonically increasing with the record ID anymore. You have to use the timestamps to order the data.
Regards,
Charles