Data Export for Power Quality Study

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Data Export for Power Quality Study
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
489
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
90
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
jedzruiz1985
Ensign jedzruiz1985
Ensign

Posted: ‎2024-10-29 06:38 PM

1 Like
8
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-29 06:38 PM

Data Export for Power Quality Study

Hi Xperts,

 

Just want to ask, if a PM8240 is connected to a PAS800L (serial connection with other meters on Modbus RTU protocol), can I still plug my laptop to the meter's ethernet port and add the meter to ION setup in order to download all historical data?  Data sampling is activated in the Panel Server therefore I can grab the data from there as well however some required data might not be ticked (sampled) that is why I am asking if I can grab them via ION setup without disrupting its normal operation.

 

The client needs to see a week long data log of power factor and THDs.

 

Furthermore, which parameters do I need to look at? is it the TotalRmsPowerFactor, FundThdVoltagePhsAN (B and C), FundThdCurrentPhsA (B and C).

 

Thanks in advance.

 

 

Jiedan

 

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
View products (1)
Labels
  • Labels:
  • PM8000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-11-06 08:30 AM . Last Modified: ‎2024-11-06 08:31 AM

0 Likes
0
997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-06 08:30 AM

Hi @jedzruiz1985 


Please note that depending on which feature set the meter has, some options are not supported. The PM8240 has a Standard feature set that does not support Flicker.
PM8000 series overview:
Mehran_Mehrnia_0-1730910164744.png

But as Charles mentioned, other CSV reports that are retrieved directly form the meter's onboard log(related Data Recorder), can be interpreted by PME.


Best Regards,

-Mehran
L3 Expert Advanced metering

See Answer In Context

Reply
Replies 8
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-10-30 08:09 AM

0 Likes
0
1117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-30 08:09 AM

Hi @jedzruiz1985 

 

Yes, ION meter such as ION7400 supports simultaneous serial and TCP communication over Modbus(PAS800) and ION(ION Setup) protocols.

Meter’s default template includes factory-configured data logs (Data Recorder modules) which can be checked in ION Setup to create a CSV report. ION Setup -> Setup Assistant -> Data Recorders

 

Mehran_Mehrnia_0-1730300422047.png

e.g Historic Average:

Mehran_Mehrnia_1-1730300964786.png

 

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
jedzruiz1985
Ensign jedzruiz1985
Ensign

Posted: ‎2024-11-03 06:46 PM

0 Likes
0
1071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-03 06:46 PM

Hi Mehran,

 

Thanks for your response. I got the data CSV file from PAS800L (from site), my next question is, can I upload this CSV file to PME 2023 to generate a power quality analysis report? We have PME with Power Quality Module in our own building so I would like to take advantage of its features. How or what is the process of uploading a CSV file from a panel server to PME? 

 

We need to generate a power quality study / report for our client. 

 

Thanks in advance.

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-11-04 08:25 AM . Last Modified: ‎2024-11-04 08:25 AM

0 Likes
0
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-04 08:25 AM

Hi @jedzruiz1985 

 

You're welcome.

I am not fully aware of all PME features, but I believe yes, it is possible to import csv file to PME using ETL(Extract Transfer Load) tool. [PME][Tool] PME ETL

 

PME2024 System Guide:

Mehran_Mehrnia_0-1730737257066.png

 

For further assistance, I would recommend that you post your question in the PME forum.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-05 09:20 AM

0 Likes
0
1028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-05 09:20 AM

Hello @jedzruiz1985 ,

 

Note that many of the reports and gadgets in PME will assume that PME is talking to the meter directly and able to get the onboard logs. Gateway like PAS800L may have some logging however this will not match the onboard logs available in PM8000 meter. Not all features of PME will work with PAS800L exported data.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
jedzruiz1985
Ensign jedzruiz1985
Ensign

Posted: ‎2024-11-05 09:48 PM

0 Likes
1
1011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-05 09:48 PM

Hi Charles,

 

So what if we extract the data directly from the meter (PM8240) via IONsetup? Question is, which data do we need to extract from the meter to satisfy the requirement of the below clauses? Does PM 8240 capture flicker? 

 

jedzruiz1985_0-1730871928393.png

 

Thanks.

 

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-11-06 08:30 AM . Last Modified: ‎2024-11-06 08:31 AM

0 Likes
0
998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-06 08:30 AM

Hi @jedzruiz1985 


Please note that depending on which feature set the meter has, some options are not supported. The PM8240 has a Standard feature set that does not support Flicker.
PM8000 series overview:
Mehran_Mehrnia_0-1730910164744.png

But as Charles mentioned, other CSV reports that are retrieved directly form the meter's onboard log(related Data Recorder), can be interpreted by PME.


Best Regards,

-Mehran
L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2024-11-06 09:16 PM

0 Likes
0
968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-06 09:16 PM

Hello @jedzruiz1985 ,

 

Is there a reason why the PM8000 cannot be connected directly to PME?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
jedzruiz1985
Ensign jedzruiz1985
Ensign

Posted: ‎2024-11-06 11:24 PM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-06 11:24 PM

Hi Charles,

 

It will be... in the control center, however, at this time, the network infrastructure is not yet ready. 

 

Regards,

 

Jiedan

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now