DCF ION7650

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • DCF ION7650
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2014-06-11 07:54 AM . Last Modified: ‎2020-04-22 01:48 AM

0 Likes
5
1503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-11 07:54 AM

DCF ION7650

For a client I had to program two identical ION7650 (370e).

I programmed in the first ION7650 with Designer (PME7.2.2).

I then saved the DCF file of this fist ION7650 to my PC with ION Setup 3.0.14094.02.

I then sent this DCF file to the second ION7650 with ION Setup.

It worked.

But...

The modules are randomly spread in groups when I open the second ION7650 in Designer.

So it is almost impossible to continue programming in the second ION7650, because now it is a real mess in Designer. Also my notes were gone.

Therefore I restored its original DCF file and I had to redo all the programming for the second ION7650.

 

Did I do something wrong? Or is this a bug that needs to be fixed?

 

 

 

(N.B.: the file name is 7650_FAC_V3.6.0.0.0.dcf and I believe the firmware version of both ION7650 is 371e.)

Labels
  • Labels:
  • ION Setup
Tags (5)
  • Tags:
  • dcf
  • ion
  • ion7650
  • setup
  • template
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
jimbradley
Lt. Commander jimbradley
Lt. Commander

Posted: ‎2014-06-12 11:17 AM

1 Like
0
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-12 11:17 AM

Hi Philippe,

Your work flow makes sense and is probably the easiest way to do things but as James pointed out there are a few tricks:

The layout of a device in Designer is not stored in the device, it is stored on the system.

When Designer firsts “opens” a meter it looks at a setup register in the device that indicates it’s default framework.

It then looks in the \system\diagram folders to find a matching Designer diagram file.

If it can not find one it creates a “default” diagram with modules placed in folders by type.

When the meter is closed in Designer the diagram file is written to \config\diagrams\nd\meter.name[serial number].cfg

The next time Designer opens a meter it will use this file for layout

So what has happened is that for your second meter because it was the first time Designer opened the meter it opened the default layout.  Then it noticed you had put in some new modules and Designer places them into a grouping object (same as a folder in Windows) called "Extra Modules" (name has changed over the years).

So to get the look in Designer for the second meter based on the first meter here is what I do:

Open the second meter in Designer.  You get all the new modules placed in the "Extra Modules" grouping object and not layed out at all.  Close the second meter in Designer. This creates a unique .cfg for that meter.

Open  \config\diagrams\nd and note the name of the file .cfg for both the first and second meter.  Make a copy of the first meter .cfg file.  Rename the second meter file to .cfg.old (or something like that), rename the copy of first meter .cfg to be second meter.cfg.  Re-open the second meter in Designer and it will use the .cfg file based on the layout of the first meter.

This sounds more complicated that it actually is.

If you are doing a lot of meters with same look you can change the register in the meter and create a folder in  \system\diagram thus generating anew "default" for you framework. This generally not worth doing.

Jim

See Answer In Context

Reply
Replies 5
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2014-06-12 06:09 AM

1 Like
2
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-12 06:09 AM

Very common oversight but easy to solve.

Unfortunately the meter itself doesn't save the folder structure or Designer layout. So when you paste the new DCF, it still has the old template referenced and will load that one and all of your graphical components from the PC stored cfg file.

You need to go into the cfg folder (inside Config of ION Enterprise folder I believe from memory here) and grab the cfg file of 7650 you first did and copy it, and rename to the second one's name (overwrite the initial one created when you first opened up in Designer).  Then the next time you open it up it will all load as per the first one.

Whallah.

Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2014-06-12 08:33 AM

0 Likes
1
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-12 08:33 AM

Thank you James,

I'll try this.

I already had a quick look, I think the cfg file is in the folder C:\Program Files (x86)\Schneider Electric\Power Monitoring Expert\config\diagrams\nd.

Reply
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2014-06-12 10:17 AM

0 Likes
0
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-12 10:17 AM

Yup! That's the one.

Reply
jimbradley
Lt. Commander jimbradley
Lt. Commander

Posted: ‎2014-06-12 11:17 AM

1 Like
0
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-12 11:17 AM

Hi Philippe,

Your work flow makes sense and is probably the easiest way to do things but as James pointed out there are a few tricks:

The layout of a device in Designer is not stored in the device, it is stored on the system.

When Designer firsts “opens” a meter it looks at a setup register in the device that indicates it’s default framework.

It then looks in the \system\diagram folders to find a matching Designer diagram file.

If it can not find one it creates a “default” diagram with modules placed in folders by type.

When the meter is closed in Designer the diagram file is written to \config\diagrams\nd\meter.name[serial number].cfg

The next time Designer opens a meter it will use this file for layout

So what has happened is that for your second meter because it was the first time Designer opened the meter it opened the default layout.  Then it noticed you had put in some new modules and Designer places them into a grouping object (same as a folder in Windows) called "Extra Modules" (name has changed over the years).

So to get the look in Designer for the second meter based on the first meter here is what I do:

Open the second meter in Designer.  You get all the new modules placed in the "Extra Modules" grouping object and not layed out at all.  Close the second meter in Designer. This creates a unique .cfg for that meter.

Open  \config\diagrams\nd and note the name of the file .cfg for both the first and second meter.  Make a copy of the first meter .cfg file.  Rename the second meter file to .cfg.old (or something like that), rename the copy of first meter .cfg to be second meter.cfg.  Re-open the second meter in Designer and it will use the .cfg file based on the layout of the first meter.

This sounds more complicated that it actually is.

If you are doing a lot of meters with same look you can change the register in the meter and create a folder in  \system\diagram thus generating anew "default" for you framework. This generally not worth doing.

Jim

Reply
Yu_Diao
Commander Yu_Diao Commander
Commander

Posted: ‎2014-06-17 02:32 PM

1 Like
0
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-06-17 02:32 PM

Another way to do it (especially for a few meters): using Desginer to save the framwork as "fwn" file, which containts all the layout AND notes and do a "locked" paste into the new meters.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of