Custom calculations with ION7650

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Custom calculations with ION7650
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-11-27 05:40 AM

0 Likes
15
2016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-27 05:40 AM

Custom calculations with ION7650

Hi,

a customer wants a few custom calculations logged in SQL database:

1) is the Urms automatically calculated in ION7650? if yes, were do i finde the value.

if not how can i calculate it?

Is this the right formular?

5311

2) were do i find Plt (Power-line flicker) and Pst this should be stored every 2 hours. (12 Pst values)

thx for help

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2014-12-03 01:07 AM

0 Likes
1
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-12-03 01:07 AM

Hello Sven

Yes, you can assign a setpoint module and link the module to the digital output of the ION meter

See Answer In Context

Reply
Replies 15
sesa256952
sesa256952 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-11-27 02:26 PM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-27 02:26 PM

You will likely need to do a bit of programming.

For programming ION meters I like to use designer in PME. It is also mandatory to have an ION reference on hand (unless you have an incredible memory)

To accomplish what you wish to do, at a minimum, you would need an arithmetic module and a data recorder module.

The arithmetic module allows you to perform the calculations and the data recorder module allows you to store and log the results.

I know it's not everything but I suspect you can work out the rest..

.

Reply
jimbradley
Lt. Commander jimbradley
Lt. Commander

Posted: ‎2014-11-27 03:14 PM

0 Likes
1
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-27 03:14 PM

Hi Sven,

Could you define the what the labels are in your equation. 

It "looks" like the "power triangle" equation for Active (real) Energy ie kW = Sqrt(kVA ^2 - kVAR^2). 

Plt and Pst are recorded IF you have the PQ framework in the 7650.  The data is stored when the Flicker module finishes a Pst (10 minutes) or Plt (120 minutes) calculation. 

These are measurements/labels recorded.

Source - FLK1 Phase 1 Pst (V1-Flck Pst)

Source - FLK1 Phase 2 Pst (V2-Flck Pst)

Source - FLK1 Phase 3 Pst (V3-Flck Pst)

Source - FLK1 Phase 1 Plt (V1-Flck Plt)

Source - FLK1 Phase 2 Plt (V2-Flck Plt)

Source - FLK1 Phase 3 Plt (V3-Flck Plt)

Note that the Plt values are analysed in the meter into "bins" with the Signal Limit Evaluation modules which are also recorded and the bin statistical values are used in the standard PME reports.

Jim

Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-11-27 11:50 PM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-27 11:50 PM

Hi Jim,

i don't know exactly because the customer only says he wants a calculation of U rms and I rms.

I found the formula on the internet. I dont know if its the right one for the calculation. 

thank you

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-11-28 01:31 AM

0 Likes
4
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 01:31 AM

Hi Sven,

After the ION7550/7650 user guide the calculated voltage is the RMS voltage:


5327

Best Regards

Daniel

Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-11-28 01:41 AM

0 Likes
3
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 01:41 AM

Hi Daniel,

do you know how these values are exactly named in the ION Device?

And are they stored with Data Recorder?

The customer wants AVG/MIN/MAX in 10 Min Interval stored.

thank you

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-11-28 01:58 AM

0 Likes
2
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 01:58 AM

Sven,

Those values are logged on the device per default:

5328

I had a look on a device in our office and there is a 15 min interval defined. I guess that this is the default interval. In this case you will have to change the logging interval to 10 min.

One remark: The RMS values are logged as mean values, what means, that this is something like a demand value (integration over a certain period -> 15 minutes; should also be changed if you like to log on 10 min interval)

Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-11-28 02:15 AM

0 Likes
1
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 02:15 AM

Hi Daniel,

yes this should all be changed to 10 min interval. Were do i find the Timer or Periodic 15 min trigger for

This should all be stored in SQL Databse:

15 Min interval:

P,Q,S, PF, cosPhi

10 Min interval:

1) U rms, Irms AVG/MAX/MIN

2) THD U, THD I, Unbalance AVG/MIN/MAX

3) Flicker: Pst in 10Min and Plt in 2h interval

4) Harmonics until 50th, voltage and power

5) Frequency: AVG/MAX/MIN

Other changes and triggers:

- Deviation of voltage +-10%, Stop at +-8%

- Change of U +-5%

- deviation of sinus pretime 1sec + posttime 3 sec

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-11-28 02:18 AM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 02:18 AM

Hi Sven,

I will send you the answer over Email - it's easier.

Daniel

Reply
Anonymous user
Not applicable

Posted: ‎2014-11-28 02:23 AM

0 Likes
6
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 02:23 AM

Hello Sven

Check this link. In it you will have the default logged values, also there is a section for the RMS values

http://www.powerlogic.com/literature/7550-7650_User_Guide_70002-0248-07.pdf

5330

Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-11-28 02:34 AM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 02:34 AM

Hi Amine,

there is only V1-3 RMS but no I RMS?

and this is stored every 3sec?

Reply
dborle
Lt. Commander dborle
Lt. Commander

Posted: ‎2014-11-28 02:36 AM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 02:36 AM

Hi Amine,

Yes, you are correct, but there are only RMS values for voltage in 40-30 and not for I.

Reply
sesa56307_bridg
Lieutenant JG sesa56307_bridg Lieutenant JG
Lieutenant JG

Posted: ‎2014-11-28 03:24 PM

2 Likes
3
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-11-28 03:24 PM

The section of the user guide that Amine shows here describes the 4-30 data logs that are in the meter's default configuration.  There are three different data logs for 3 second values, 10 minute values, and 2 hour values.  Each of those three logs contains most of the 4-30 parameters listed in the right column (voltage disturbances and flicker are actually stored in other logs).  So there should be 10-minute values for V1-3 RMS in the 10-minute log (where the values correspond with the 4-30 definition for 10-minute aggregation intervals, which does use an RMS algorithm).

Regarding the question about 10-minute values for I1-3 RMS, the meter does calculate these values, but they are not included in the default log.  In the ION framework, you can find the 10-minute values for current as output registers on the Power Quality Aggregator module.  They are not logged because (as Daniel noted) there is no normative definition for these parameters in the currently published edition of 4-30 (though an upcoming edition of 4-30 is expected to add this).  If you want to log these 10-minute current values (so they are accessible in the SQL database), you should be able to customize your ION framework to add this functionality in a new log.  Or alternatively, you could use the data from the Hist Mean Log mentioned in an earlier comment (which just provides an arithmetic average of the one-second RMS values), and adjust the framework to use a 10 minute interval instead of the default 15 minute interval.

Best regards,

David Tuckey

Firmware Architect

Reply
Sven_Ortmann
Sven_Ortmann Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-12-03 12:42 AM

0 Likes
2
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-12-03 12:42 AM

thank you all for the help and answers

i have another question:

is it possible to enable a potential-free contact with ION7650 if one of these Events is outside the tolerance:


- Deviation of voltage +-10%, Stop at +-8%

- Change of U +-5%

- deviation of sinus pretime 1sec + posttime 3 sec

Reply
Anonymous user
Not applicable

Posted: ‎2014-12-03 01:07 AM

0 Likes
1
1913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-12-03 01:07 AM

Hello Sven

Yes, you can assign a setpoint module and link the module to the digital output of the ION meter

Reply
Hal_Etheridge
Janeway Hal_Etheridge Janeway
Janeway

Posted: ‎2014-12-03 10:05 AM

0 Likes
0
1912
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-12-03 10:05 AM

For more complex logical conditions it is also possible to chain multiple setpoint modules together in an arbitrary order using And/Or modules.  The configuration could be multiple setpoint modules (all monitoring a single condition) with their status outputs connected to a single And/Or module (that evaluates the combined status of the alarms) that and is input to another setpoint that that generates the final overall alarm status that you then monitor in the SW (or link to a digitial output, etc).  Obviously you probably would want to change the event priority of the initial input setpoint modules to be zero or other low number to avoid generating alarms when they trigger (unless you are interested in when the preconditions trigger as well as the final output).

Remember that ION is like a big box of lego - lots of little pieces that can be assembled in whatever order you want to solve the big problem.  There are nearly always multiple ways to solve a problem so the above solution is just one of the possibilities.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of