I need help with reading PMxxxx registers in float32.
Link copied. Please paste this link to share this article on your social media post.
Hello @Smartwatt12 ,
A little context here will go a long way. Are you talking about modbus registers? Often with 32 bit registers in modbus, the word order is important. Some devices, the high word is first and other devices the low word is first, once you determine that the float usually follows IEEE 754 float format.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Smartwatt12 ,
A little context here will go a long way. Are you talking about modbus registers? Often with 32 bit registers in modbus, the word order is important. Some devices, the high word is first and other devices the low word is first, once you determine that the float usually follows IEEE 754 float format.