Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Consultation to change firmware to a previous version

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Consultation to change firmware to a previous version
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Ricardo_RM
Ricardo_RM
Contributor

Posted: ‎2024-05-24 11:39 AM . Last Modified: ‎2024-05-24 11:40 AM

0 Likes
7
3808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-24 11:39 AM

Consultation to change firmware to a previous version

Hello community,

A few days ago the firmware of some ION7650 was updated to version V416, but the customer noticed that they do not provide communication to some systems that have other than the PME such as the DCIM.

 

They want to lower the version to what they had, which was V415. But I have read that this is not good practice because it can damage the meter.

 

I wanted to know if the firmware version can be changed to the previous one without problems or if there is some degree of danger that it could damage the equipment.

 

Greetings

 

@Charles_Murison 

Labels
  • Labels:
  • ION7000
Tags (2)
  • Tags:
  • english
  • spanish
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-05-31 12:07 PM

0 Likes
0
3663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-31 12:07 PM

Hello @Ricardo_RM ,

 

Modules offline should not affect communications, there could be something else happening there. Hard to troubleshoot something like this from the forum. One item to note is ION7650 meters are obsolete so there may be limited technical support options. I would start with using a V415 default template to see if that works on the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 7
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2024-05-26 11:08 PM . Last Modified: ‎2024-05-27 12:08 AM

1 Like
1
3771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-26 11:08 PM

Hi @Ricardo_RM 

 

Downgrade to lower version V415 is supported and does not damage the meter, however, as mentioned in 'WHAT'S NEW' note of V416 release, number of new features and changes that are designed to help improve the security of the meter, will be removed.

If you have customized Framework, before downgrade/upgrade, please take a backup using ION Setup(Setup Assistant -> Template -> Save to PC), and paste it again during downgrade/upgrade process.

 

There is another option to upgrade/downgrade only the firmware by holding <Ctrl> + clicking on upgrade button, which will prompt a message to just do firmware upgrade.

Mehran_Mehrnia_0-1716793651021.png

 

Best Regards,

-Mehran

L3 Expert Tech Support

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-05-28 08:56 AM

2 Likes
0
3744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-28 08:56 AM

Note that if doing a firmware only upgrade, after then upgrade is complete, the meter will have no template, no display screens, no logging, no frameworks etc. You will want to apply a template to the meter after the upgrade is complete.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2024-05-28 10:00 AM

3 Likes
0
3742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-28 10:00 AM

Also be warned that attempting to download any template from *newer* firmware to older firmware (V416 -> V415 firmware) may possibly cause issues when doing so.  It is preferable to either use a previously saved template (one which was saved when the device was set to V415 firmware) or use the factory default one (and then manually updating the device changes again).  There are ways to force the use of the template but possible new template changes won't possibly exist on the older firmware so this could lead to lots of issues.

Reply
Ricardo_RM
Ricardo_RM
Contributor

Posted: ‎2024-05-30 06:28 AM . Last Modified: ‎2024-05-30 06:29 AM

0 Likes
3
3705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-30 06:28 AM

Hello, thank you very much for the answers.

 

We did the test with a 7650 meter, but when downloading for the first time this error appears.

 

Ricardo_RM_0-1717075415824.png

 

 

The meter also goes blank, but if it is turned off and on again it returns to normal.

 

Ricardo_RM_2-1717075532417.jpeg

 

Ricardo_RM_3-1717075637895.png


And checking if they have the correct firmware version, but if it shows some messages in ION Setup like the following

 

Ricardo_RM_4-1717075689814.png

 

Do you think this may affect communications?


Greetings

 

@Robert_Lee  @Charles_Murison @Mehran_Mehrnia 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-05-30 09:27 AM

0 Likes
2
3697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-30 09:27 AM

Hello @Ricardo_RM ,

 

This is part of what we have been talking about, templates are usually future firmware compatible, not always backward firmware compatible. A template from V410 firmware is likely to work on V415 or V416 firmware however a V416 template is unlikely to work on V410 firmware.

RMP stands for rapid meter programming, This will configure the meter completely before taking all the modules online, if any module fails to go online you get that message. You meter will still communicate however many, if not all modules, are offline, no data recording, no display modules, no min/max, no demand etc. Most of the features of an ION meter comes from the template.

When you restarted the meter, many of the modules came online however there may still be some modules offline. You many need to do a check with ION Setup again.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Ricardo_RM
Ricardo_RM
Contributor

Posted: ‎2024-05-30 09:53 AM

0 Likes
1
3696
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-30 09:53 AM

Hello @Charles_Murison 

 

I understand, regarding this point I clicked on the Online option that appears in the image and that message no longer appeared.

 

Ricardo_RM_0-1717087976460.png

 

 

We also tried to load the firmware again, but the same error appeared.

 

But it could be because of what you mentioned. And the customer has a DCIM system where the meter was no longer communicating, it may be a product of these modules not starting correctly.

 

Greetings.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-05-31 12:07 PM

0 Likes
0
3663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-31 12:07 PM

Hello @Ricardo_RM ,

 

Modules offline should not affect communications, there could be something else happening there. Hard to troubleshoot something like this from the forum. One item to note is ION7650 meters are obsolete so there may be limited technical support options. I would start with using a V415 default template to see if that works on the meter.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.