New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Connecting ION7650 with RS485 liaison
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2015-09-0803:49 AM
Connecting ION7650 with RS485 liaison
Hi All,
Is it possible to connect an ION7650 ( without Ethernet port ) to the server ( PME 7.2 ) with RS485 liaison for a long distance ( less than 1000 meters) ? if so, this ION7650 will be able to communicate in ION protocole ?
Link copied. Please paste this link to share this article on your social media post.
2016-04-1911:39 PM
Quite an old question but I will answer. Yes you can the max. distance for RS-485 is 1000 meters but you might have to adjust some communication parameters a bit.
Link copied. Please paste this link to share this article on your social media post.
2016-04-1911:39 PM
Quite an old question but I will answer. Yes you can the max. distance for RS-485 is 1000 meters but you might have to adjust some communication parameters a bit.