Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84243members
353342posts

Connect PM1000 to PME2021

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
SESA_B
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
1
495

Connect PM1000 to PME2021

Hi admin,

 

My customer have PM1000. I saw PM1000 have port communication RS485 (Pin 7_[ D1+] and Pin 14_[D0-] in attached image). But when i connect to PME2021, i can't read data. Pls help me.

 

Thanks very much.

 

IMG_4124.JPGIMG_4133.JPG

Tags (1)

Accepted Solutions
Robert_Lee
Captain Captain
Captain
0 Likes
0
411

Re: Connect PM1000 to PME2021

In most cases, to connect a serial device (RS-485) to PME (or any PC-based software), unless the device is within physical proximity to the device *or* existing RS-485 wiring is available (to a maximum of 5000 ft I believe), then the best option is to use some type of Modbus TCP gateway device (like EGX-150/Link 150) that allows a PC to use network TCP Modbus which can then be wired to RS-485 devices.

Usually those devices have a web interface that allows you to properly configure the RS-485 port on the gateway to match up with the settings programmed in any device to allow proper communications.

[Edit]

Upon further investigation, the PM1000 does not come with standard Modbus communications (only a DO which can be used for energy pulsing).  The PM1200 is the one that has RS-485 communications (see attached differences between the two models).

https://www.se.com/ww/en/product-range/7206-easylogic-pm1000-series/#overview

 

See Answer In Context

Attachments
Tags (1)
1 Reply 1
Robert_Lee
Captain Captain
Captain
0 Likes
0
412

Re: Connect PM1000 to PME2021

In most cases, to connect a serial device (RS-485) to PME (or any PC-based software), unless the device is within physical proximity to the device *or* existing RS-485 wiring is available (to a maximum of 5000 ft I believe), then the best option is to use some type of Modbus TCP gateway device (like EGX-150/Link 150) that allows a PC to use network TCP Modbus which can then be wired to RS-485 devices.

Usually those devices have a web interface that allows you to properly configure the RS-485 port on the gateway to match up with the settings programmed in any device to allow proper communications.

[Edit]

Upon further investigation, the PM1000 does not come with standard Modbus communications (only a DO which can be used for energy pulsing).  The PM1200 is the one that has RS-485 communications (see attached differences between the two models).